    mitsu pulling a vac



    hi

    have an intermitting problem with a mr slim 407c puh-5kygaa... i keep getting a uh ,u2 error which is a compressor abnormal fault...due to possible high amps or insufficent cooling to compressor

    checked pressures and found suction in a vac and liquid line cool in cool mode ....there is an lev on the outdoor unit which i suspect may be a bit dodge...

    however i switched unit into heat mode and the pressures/temps where fine so switched back to cool and away it went...has anyone have something simular like this happen?do you reckon moisture ? this system has been running for years until now...

    rgrds phil



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: mitsu pulling a vac

    ok i had a few of these years ago and the lithium expansion valve head(think thats what they call it) on the condenser was over tightened to the body,half a turn and wosh!! pressures back to normal! they didnt show on commissioning (funny that) but on the first service one month after,failing that it could be a blocking? or 4 way vavle?

    iam well out of practise with mitsi but sure one of the mitsi will be along soon
    Last edited by superswill; 28-04-2008 at 09:29 PM.
    Paul


    "KEEP IT COOL"

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: mitsu pulling a vac

    Hi Phil

    Next time it happens get down to the evaporator and check the flare connections inside the unit.

    You'll probably find that it is frozen/frosted over.

    If you have both gauge lines connected on the downstream side of the condensing unit then shut the liquid line, open your gauges and pump down the evaporator.

    Open the flare connector and remove the frozen waxy ice from the strainer inside the male flare.

    Ideally blow through with some OFN, fit a filter/drier, vac out and open your service valves and you could be OK.

    [edit] If not then try the LEV.
    Last edited by Brian_UK; 29-04-2008 at 12:11 AM. Reason: Spelling, of course!
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Mar 2006
    Location
    Australia
    Posts
    28
    Rep Power
    0

    Re: mitsu pulling a vac

    could be a blockage, when u switch the unit onto heating, the refrigerant starts flowing the other way which dislodges whatever is causing the blockage, just an idea

Similar Threads

  1. mitsu indoor problem
    By philjd26 in forum Air Conditioning
    Replies: 9
    Last Post: 12-11-2007, 05:12 PM
  2. mitsu heavy inds remote display
    By dirker in forum Heat Pumps
    Replies: 1
    Last Post: 08-04-2007, 10:54 PM
  3. Mitsu Heavy Industry
    By bobjob in forum Air Conditioning
    Replies: 1
    Last Post: 14-07-2005, 11:00 PM
  4. Mitsu faults
    By Abe in forum Air Conditioning
    Replies: 2
    Last Post: 31-03-2003, 07:30 AM
  5. Mitsu
    By Abe in forum Air Conditioning
    Replies: 11
    Last Post: 05-01-2003, 02:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •