    Two stage ammonia system



    We are expecting a project for Ice Cream The system has to be with NH3. The total heat load has been assessed by us is 15 TR at -38 oC Te and 40 oC Tc.

    We are planning to use one Vilter-Frick India reciprocating open type 2 stage compressor. There shall be 2 nos of Evaporators inside the room, each of 50% of the totl load. The Condenser shall be of the Evaporative Type.

    I am not much aware of NH3 plants and whatever I have learnt is from this forum. Now prior to the finalisation of the project, I would like to prepare myself. What I have learnt from the RE, that for such application, Liquid Overfeed is very effective. How do I assess the capacity of the Liquid pump ? I presume One pump shall be suffecient to for the 2 Evaporators.

    Since importing the vessels would be very expensive, I would also like to know the details of the vessels required so that accordingly i may get it constructed here. The Evaporator shall be imported.

    There will be more questions, and your patience and reply shall be highly appreciated.



  2. #2
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: Two stage ammonia system

    The system design is not very difficult, but I have found that i need a min of 3 evaorators at low temp to make enough defrost gas for the defrosting of a evaporator. I can send a few vessel details that you can use for a typical recirculator with a pump. Send me an email address and I will forward a few details from our Recirculator vessel designs.

    Best to you

    Bruce

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,016
    Rep Power
    19

    Re: Two stage ammonia system

    Dear Bruce,

    We propose to use two Evaporators and have electric defrost system.

    You may send the details to me via a PM

    I shall be keenly awaiting your reply.

    Thank you.
    Last edited by chillin out; 27-04-2008 at 03:05 PM. Reason: Please do not post e-mails.

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,016
    Rep Power
    19

    Re: Two stage ammonia system

    Hi Bruce,

    I have sent a PM to you. Rearding the Defrost, we propose to use electrcic defrost.

    Hope to hear from you soon.

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,016
    Rep Power
    19

    Re: Two stage ammonia system

    Hello Chillin Out,

    I am sorry to have put my e mail id as I know very well that the same should not be put. But then I would like to point out that there are a large number of posts where the e mail ids have been put for getting the relevant informations.

    Maybe due to oversight they were not removed.

  6. #6
    Join Date
    May 2008
    Location
    Singapore
    Posts
    26
    Rep Power
    0

    Re: Two stage ammonia system

    maybe i can help too, but i think instead of using electric defrosting, why not just use hot gas defrosting, so much easier. design a 3 line system. i can send you a rough design, PM me ok

  7. #7
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Two stage ammonia system

    Hi samarjit,

    so you are using liquid overfeed with pump. ...

    i've experienced ice cream plants in DX design.

    would you consider that?

    yeah, vessel is pretty expensive these days every where. better to do it locally. good choice!

    but you must know the design. some suppliers may give you non Ammonia design. so be careful.

    how about your intercooler? open flash type you use?

    anyway, i know you are capable to solve the problems. hope my questions induce further evaluation.

    Hendry, on wesak day holiday.
    Hendry

    "What uncertainty means to you, and you only?"

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Two stage ammonia system

    Hi,

    Quote Originally Posted by kelvin_27_84 View Post
    maybe i can help too, but i think instead of using electric defrosting, why not just use hot gas defrosting, so much easier. design a 3 line system. i can send you a rough design, PM me ok
    Quote Originally Posted by hendry View Post
    Hi samarjit,
    so you are using liquid overfeed with pump. ...
    i've experienced ice cream plants in DX design.
    would you consider that?
    yeah, vessel is pretty expensive these days every where. better to do it locally. good choice!
    but you must know the design. some suppliers may give you non Ammonia design. so be careful.
    how about your intercooler? open flash type you use?
    anyway, i know you are capable to solve the problems. hope my questions induce further evaluation.
    Hendry, on wesak day holiday.
    please, check this

    http://www.refrigeration-engineer.co...ad.php?t=12866

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    May 2008
    Location
    at the edge of the Arabian Sea!
    Age
    73
    Posts
    37
    Rep Power
    0

    Re: Two stage ammonia system

    I may suggest that you refer to some technical literature by ASHRAE or atleast have a look at books authored by Steve Elonka
    I learnt much from his books when I came across industrial refrigeration!
    all the best

  10. #10
    Join Date
    Jan 2010
    Location
    iran
    Age
    50
    Posts
    5
    Rep Power
    0

    Re: Two stage ammonia system

    We are expecting a project for Ice Cream The system has to be with NH3. The total heat load has been assessed by us is 15 TR at -38 oC Te and 40 oC Tc.

    We are planning to use one Vilter-Frick India reciprocating open type 2 stage compressor. There shall be 2 nos of Evaporators inside the room, each of 50% of the totl load. The Condenser shall be of the Evaporative Type.

    I am not much aware of NH3 plants and whatever I have learnt is from this forum. Now prior to the finalisation of the project, I would like to prepare myself. What I have learnt from the RE, that for such application, Liquid Overfeed is very effective. How do I assess the capacity of the Liquid pump ? I presume One pump shall be suffecient to for the 2 Evaporators.

    Since importing the vessels would be very expensive, I would also like to know the details of the vessels required so that accordingly i may get it constructed here. The Evaporator shall be imported.

    There will be more questions, and your patience and reply shall be highly appreciated.

  11. #11
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Two stage ammonia system

    For such a small system, a Flooded design would be much more economical than pump recirculated. Hot Gas defrost will require at least 3 evaporators so you're probably best served by electric defrost. DO NOT USE DX. IT WILL NOT WORK WELL AT THESE TEMPERATURES.
    Last edited by charlie n; 17-01-2010 at 03:07 AM. Reason: Error

  12. #12
    Join Date
    Jan 2010
    Location
    USA
    Posts
    41
    Rep Power
    0

    Re: Two stage ammonia system

    personal stuff sorry
    Last edited by jaysephus; 04-02-2010 at 06:45 PM. Reason: personal stuff sorry

  13. #13
    Join Date
    Jan 2010
    Location
    iran
    Age
    50
    Posts
    5
    Rep Power
    0

    Re: Two stage ammonia system

    Hi Dears
    I Have a question:
    1.how can i calculate separator&receiver(or some tank like accumulator ,intercooler,..) volume in double stage ammonia system?
    thanks for your kindly attention

  14. #14
    Join Date
    Jan 2009
    Location
    INDIA
    Posts
    40
    Rep Power
    0

    Re: Two stage ammonia system

    Please give a brief description of your system. what type of separator are you using ?? is it a oil seperator ??

Similar Threads

  1. Refrigeration System with Ammonia
    By Samarjit Sen in forum Refrigerants
    Replies: 71
    Last Post: 02-12-2010, 12:03 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. Single stage refrigeration system optimizing diagram
    By autt in forum System Optimization
    Replies: 34
    Last Post: 03-12-2008, 04:13 PM
  4. Ammonia Transfer System
    By gwapa in forum NH3
    Replies: 25
    Last Post: 01-05-2008, 08:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •