23-04-2008, 07:15 PM #1
u9/ue daikin fault
hi.
have a problen with a daikin vrv k series system from time to time, i have a u9 being displayed on a central controller with all associated indoors flashing same and a ue on the time schedule,it resets then after a while .. pointers anyone?
rgrds phil
-
23-04-2008, 07:27 PM #2
-
23-04-2008, 08:23 PM #3
Re: u9/ue daikin fault
Spot on Super
U9 normally occurs when the outdoor loses comms with one or more of the indoor units.
Most probable causes are:
1 - Indoor isolator switched off to one of the fan coils
2 - Comms wiring taken through the high float limit switch on the cond. pump
As it's flashing all of the indoors on the central controller, you should look at the indoor ring main power supply and also the 2 core interconnect wiring between the outdoor and the first fan coil.
The UE fault code indicates a break in the comms between the central controller and the indoor unit.
Try to trace the wiring or install a temporary 2 core to eliminate the problem
does the system have any 'add on' pcb's installed?Last edited by frank; 23-04-2008 at 08:28 PM.