Thread: Temperature drop in condenser
-
23-04-2008, 03:58 PM #1
Temperature drop in condenser
Hi, i would like to know the avarege temperature difference the air entering the condenser and the temperature of the air leaving out the condenser.
Thanks alot
Kris
-
24-04-2008, 12:18 AM #2
Re: Temperature drop in condenser
Probably around 10 c but would depend on duty and ambient temperature condenser coil cleanliness etc
-
24-04-2008, 09:25 AM #3
Re: Temperature drop in condenser
I would agree with Philfridge around 5 to 10
-
30-04-2008, 10:01 AM #4
Re: Temperature drop in condenser
Normally we design on 30 F temperature difference but what we usually get uin practical is 20-25 F IN/OUT difference
Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
-
18-05-2008, 04:41 AM #5
Re: Temperature drop in condenser
Hi sullie,
sorry but i do not know whether your condenser means air cooled OR water cooled OR hybrid type.
anyway, i learn it has direct relation to the web bulb temperature in ambient of installation.
narrow temp difference = bigger coil and vice versa.
it is economy of scale we should look into.
design is very subjective. but for air cooled, i use dT of 15K normally. BUT, do not neglect wet buld temp; it is important.
hope that helps.
Hendry, on wesak day holiday.Hendry
"What uncertainty means to you, and you only?"
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM -
re ref. circuit
By shsalameh in forum FundamentalsReplies: 5Last Post: 06-08-2007, 12:59 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM