Thread: R22 replacement

  1. #1
    Join Date
    Apr 2008
    Location
    Huddersfield
    Posts
    16
    Rep Power
    0

    R22 replacement



    I am working on a project to Replace R22 in multiple medium and low temperature evaporators in a commercial enviroment. After much research i have found that no-one seems to have any distinct answers to this quirey. The nearist i have come to a replacement is R417A, however it seems this is used mainly for a/c systems. Could this possibly be used as a sutiable replacement and if not could anyone surgest any others? I would greatly appreciate some feedback. Thank you

    Bradley SD
    BJA trainiee Refrigeration design engineer



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: R22 replacement

    r507, if the compressors are hermetic and have mineral oil it could be a pain to retrofit though.
    Nearly every system made in the last 4 years here for med and low temp has been 404a or 507
    Last edited by paul_h; 22-04-2008 at 11:55 AM.

  3. #3
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    515
    Rep Power
    18

    Re: R22 replacement

    R434a(RS45)

    Looks good

    http://www.refsols.com/RS-45.html
    If it ain't broke, it doesn't have enough features yet.


    Damo

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: R22 replacement

    I'm looking at using R-507 as a replacement for R-22 on a similar project. It looks like it will have some issues as paul_h also mentioned, but I believe these are not insurmountable.

    I would also rather use an azeotrope to eliminate the glide temperatures and fractionation issues.
    If all else fails, ask for help.


  5. #5
    Join Date
    Apr 2008
    Location
    Huddersfield
    Posts
    16
    Rep Power
    0

    Thumbs up Re: R22 replacement

    Ive ran R507a through microcalc and come up with some pretty convincing performance results . however the power usage is a little more then i bargend for and the extra superheat (%) is double that of R22 (mind you depends how much you trust an anyliser), iul compare to R434a and get back to ya. cheers iceman!

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: R22 replacement

    The impact of the power might be reduced by using a slightly larger condenser. Yeah, I know it costs more initially but in the long run I suspect it will be more cost effective if you included all the time messing around with the zeotropes or other alternatives.

    Keep us posted on your findings. You might find something useful for the rest of us.
    If all else fails, ask for help.


  7. #7
    Join Date
    Apr 2008
    Location
    Huddersfield
    Posts
    16
    Rep Power
    0

    Re: R22 replacement

    good point, thanks, what did i do without this forum!

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: R22 replacement

    Quote Originally Posted by brad__34 View Post
    good point, thanks, what did i do without this forum!
    Get more work done while you're in the office ??
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2008
    Location
    Huddersfield
    Posts
    16
    Rep Power
    0

    Re: R22 replacement

    shhhh! i dont think the techie blokes caught on yet , And besides its office related.... honest, *shifty eyes*
    The computer made me do it! :p

  10. #10
    Join Date
    Apr 2008
    Location
    The Netherlands
    Age
    49
    Posts
    67
    Rep Power
    16

    Re: R22 replacement

    Did anyone hear of the ISCEON Range of Du Pont.
    We are testing it on a small R-22 pump system now.

    No oilchange, no gasket change (allthough some broke) and no change in components.

    Still running after 5 week now.

  11. #11
    LowTemp-10F's Avatar
    LowTemp-10F Guest

    Re: R22 replacement

    i work on the supermarket refrigeration..we used R422d (mo29) to replace R22. check dupont website.

  12. #12
    Join Date
    Apr 2008
    Location
    Huddersfield
    Posts
    16
    Rep Power
    0

    Re: R22 replacement

    Quote Originally Posted by Bart Nabbe View Post
    Did anyone hear of the ISCEON Range of Du Pont.
    We are testing it on a small R-22 pump system now.

    No oilchange, no gasket change (allthough some broke) and no change in components.

    Still running after 5 week now.
    Would you call this a worthy replacement then bart nabbe? ive looked up the Du pont range but i cant desifer between ISCEON 79,59 and 29?
    The computer made me do it! :p

  13. #13
    Join Date
    Apr 2008
    Location
    The Netherlands
    Age
    49
    Posts
    67
    Rep Power
    16

    Re: R22 replacement

    Hello Brad,

    We are using MO29 (R422d) for the test.
    It is a test with the customer and supplier and ourselfs to look for good and easy replacements for Pumpsystems with R-22.

    This becuase you only know if it works when you try it.
    We want to wait untill summer (hot hahaha)to make a good (or bad) report on the test but so far so good.

  14. #14
    Join Date
    Apr 2008
    Location
    Huddersfield
    Posts
    16
    Rep Power
    0

    Re: R22 replacement

    Hey Bart, thanks for the feedback... Ive just had Mark Huges (sales manager for ISCEON) on the phone and hes told me all about the stuff ... case studies, tests in germany blah blah, relaible, blah, plentiful, you could say im sold...lol

    thanks again
    Bradley SD
    The computer made me do it! :p

  15. #15
    Join Date
    Sep 2007
    Location
    Philippines
    Posts
    12
    Rep Power
    0

    Re: R22 replacement

    drop in replacement for R22 i think is RS-44

  16. #16
    puffanflash's Avatar
    puffanflash Guest

    Re: R22 replacement

    Quote Originally Posted by brad__34 View Post
    I am working on a project to Replace R22 in multiple medium and low temperature evaporators in a commercial enviroment. After much research i have found that no-one seems to have any distinct answers to this quirey. The nearist i have come to a replacement is R417A, however it seems this is used mainly for a/c systems. Could this possibly be used as a sutiable replacement and if not could anyone surgest any others? I would greatly appreciate some feedback. Thank you

    Bradley SD
    BJA trainiee Refrigeration design engineer
    hi what about refrigerant name FORANE FX90
    RB411B CARE 50 R1270 R290 R417A GOOD LUCK
    THE ICE MAN

  17. #17
    puffanflash's Avatar
    puffanflash Guest

    Re: R22 replacement

    HI
    Look at FOREANE FX90 R411B CARE 50 R1270 R290 R417A GOOD LUCK HOPR IT HELPS


    Quote Originally Posted by US Iceman View Post
    I'm looking at using R-507 as a replacement for R-22 on a similar project. It looks like it will have some issues as paul_h also mentioned, but I believe these are not insurmountable.

    I would also rather use an azeotrope to eliminate the glide temperatures and fractionation issues.

  18. #18
    Join Date
    May 2008
    Location
    UK
    Posts
    17
    Rep Power
    0

    Re: R22 replacement

    For information on R22 replacements visit gas2010.com

  19. #19
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: R22 replacement

    Quote Originally Posted by puffanflash View Post
    HI
    Look at FOREANE FX90 R411B CARE 50 R1270 R290 R417A GOOD LUCK HOPR IT HELPS
    Although the hydrocarbons are good refrigerants, I would not recommend them for normal public use.

    We have a difficult time with using the refrigerants we have on the market without compounding the issue of flammability and other issues common to hydrocarbon refrigerants.
    If all else fails, ask for help.


  20. #20
    Join Date
    Jun 2008
    Location
    San Francisco County
    Posts
    7
    Rep Power
    0

    Re: R22 replacement

    How about Mycoms. I have 2 FW6 Receipts with water cooled heads. My head pressure runs around 175 with the tower...At the end of the year I will need to switch refrigerants..On Mycoms what do you think about Refrigerants

  21. #21
    Mr.Blue's Avatar
    Mr.Blue Guest

    Talking Re: R22 replacement



    Look Here Friends;
    There are 3 choices in this family for your consider

    R417a composition is
    R125, R134a, R600
    46.6%, 50%, 3.4%
    design for household air-con

    R422d composition is
    R125, R134a, R600a
    65.1%, 31.5%, 3.4%
    design for household air-con, refrigeration

    R422a composition is
    R125, R134a, R600a
    85.1%, 11.5%, 3.4%
    design for refrigeration, chiller

    More R125 more capacity
    More R134a more COP
    R600 & R600a the reason why no oil change its made compatible between HFC to Mineral oil.

    We will be back, friends
    Mr.Blue

  22. #22
    Join Date
    Apr 2006
    Location
    India
    Posts
    6
    Rep Power
    0

    Re: R22 replacement

    Hey guys
    This is Rohit, do anybody have comparison of R22 and R404A system design and performance>

    Pls let me know

  23. #23
    Join Date
    Sep 2008
    Location
    Belguim
    Age
    64
    Posts
    17
    Rep Power
    0

    Re: R22 replacement

    Hi Iceman,Brad 34

    Have you got some good results on your research on R434a?
    If all these people on the forum are very experienced, i can't understand that R434a is not looked at more...
    To me it seems one of the best replacements for R22 at this moment.
    I really like to here all your expertise on this matter. Because I might be using it to retrofit a DX glycol chiller

  24. #24
    ekeller's Avatar
    ekeller Guest

    Re: R22 replacement

    Quote Originally Posted by brad__34 View Post
    I am working on a project to Replace R22 in multiple medium and low temperature evaporators in a commercial enviroment. After much research i have found that no-one seems to have any distinct answers to this quirey. The nearist i have come to a replacement is R417A, however it seems this is used mainly for a/c systems. Could this possibly be used as a sutiable replacement and if not could anyone surgest any others? I would greatly appreciate some feedback. Thank you

    Bradley SD
    BJA trainiee Refrigeration design engineer
    422d direct drop in

  25. #25
    Join Date
    May 2010
    Location
    Odessa, TX
    Age
    55
    Posts
    9
    Rep Power
    0

    Re: R22 replacement

    Dupont's MO99 does not need an oil change and it works pretty good in medium temp applications and a/c

  26. #26
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    29
    Rep Power
    0

    Re: R22 replacement

    MO29 works ok but tends to cause lots of leaks due to shrinking or drying up o rings and gaskets ..... we have learnt the hard way and it has cost us alot of money to go round swapping these things to resolve the issues

  27. #27
    ron1800's Avatar
    ron1800 Guest

    Re: R22 replacement

    Quote Originally Posted by brad__34 View Post
    I am working on a project to Replace R22 in multiple medium and low temperature evaporators in a commercial enviroment. After much research i have found that no-one seems to have any distinct answers to this quirey. The nearist i have come to a replacement is R417A, however it seems this is used mainly for a/c systems. Could this possibly be used as a sutiable replacement and if not could anyone surgest any others? I would greatly appreciate some feedback. Thank you

    Bradley SD
    BJA trainiee Refrigeration design engineer
    depending on your operating conditions you could lose up to 28% capacity on low temp and roughly 20 percent on medium temperature with 417A. if you have that much excess capacity. it should work but i would be cautious with oil return using mineral oil, if you have good oil seperators and short piping runs and no receiver it should work, if not you will see oil in the receiver and must start adding POE oil to get good return. better path is to use an HFC with better capacity and switch to synthetic lube. hope this helps.

  28. #28
    ron1800's Avatar
    ron1800 Guest

    Re: R22 replacement

    Quote Originally Posted by surenuff View Post
    Dupont's MO99 does not need an oil change and it works pretty good in medium temp applications and a/c
    Sure will work better than 417 from a capacity perspective, i think my comments about oil return with 417 would still hold true with this blend as well. you need to check the oil return and add poe if it is slow. DuPonts and copelands application bulletins indicate this.

  29. #29
    zebraveheart's Avatar
    zebraveheart Guest

    Re: R22 replacement

    Hi there
    I am droping in R422D in plants until 400 kgs of refrigerant.
    No problems at all.
    I am very impressed about.

Similar Threads

  1. R 417 A direct replacement of R 22
    By abbasi in forum Refrigerants
    Replies: 28
    Last Post: 08-09-2011, 12:47 AM
  2. new r22 drop-in replacement
    By nh3simman in forum Refrigerants
    Replies: 46
    Last Post: 04-06-2010, 07:44 PM
  3. HFC Replacement for r22 in flooded system
    By kevinM in forum Refrigerants
    Replies: 8
    Last Post: 26-03-2008, 03:02 PM
  4. Replacement Screw Compressors
    By dkemper in forum Technical Discussions
    Replies: 2
    Last Post: 13-10-2007, 07:22 PM
  5. F 11 replacement for flushing