    Suction accumulators



    Hello

    I read somewhere that suction accumulators can be useful in plated heat exchanger systems since with these plates the liquid refrigerant tends to condesate when the compressor is off.

    Why liquid receiver tends to condensate when compressor is off? can anyone explain?

    thanks



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Suction accumulators

    What actually happens on some systems (without a solenoid valve in the liquid line and pump down to stop) is that the plate heat-exchanger used as evaporator fills up with liquid as it's the coldest part of the circuit. When the compressor then starts, it will try and compress liquid refrigerant...

    A suction accumulator will reduce the risk of liquid reaching the compressor (so would a proper pumpdown)

  3. #3
    Tjune54's Avatar
    Tjune54 Guest

    Cool Re: Suction accumulators

    To answer your second question; with out a soleniod valvle for pump down. The refrigerant will continue to migrate to the coldest prt of the system (cold plates).
    When the level lquid level in the receiver drops below the king valve intake the refrigerant starts to boil and absorb heat. Thus dropping the tank below dewpoint and condensating where liquid touches the sides.

  4. #4
    Join Date
    Apr 2008
    Location
    Germany
    Age
    55
    Posts
    10
    Rep Power
    0

    Re: Suction accumulators

    Thanks a lot to both

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Suction accumulators

    What's King Valve?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Suction accumulators

    The shutoff service valve on the receiver outlet

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Suction accumulators

    Quote Originally Posted by Peter_1
    What's King Valve?
    Peter, the king valve is the valve on the receiver that controls the liquid flow to the system (like wambat said).

    I have never heard an explanation of how this valve came to be named this though?
    If all else fails, ask for help.


Similar Threads

  1. Copeland select 6
    By Copman in forum Tools and Calculators
    Replies: 9
    Last Post: 27-05-2010, 09:01 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Should suction accumulators be insulated?
    By superheated in forum Commercial
    Replies: 7
    Last Post: 16-02-2008, 07:12 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. Suction Accumulators
    By rsiyer in forum Technical Speculations
    Replies: 2
    Last Post: 15-06-2007, 04:16 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •