    Digital scroll



    Hi,
    I'm new in this forum and in this field/market

    has anyone heard about Copeland digital scroll and its performance in hydronic systems (chillers / heat pumps)?

    any idea on how to control it? how would you drive the EXV given the pulsating nature of the compressor?

    thanks fo your help



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Digital scroll

    Try to find something from this manual:
    http://tinyurl.com/65v5xh

  3. #3
    Join Date
    Apr 2008
    Location
    Germany
    Age
    55
    Posts
    10
    Rep Power
    0

    Re: Digital scroll

    Thanks a lot nike123

    this is a manual for a VRF system, multievaporators, very interesting

    any idea if there is something available also for hydronic, single evaporator systems?

  4. #4
    Join Date
    Apr 2008
    Location
    Germany
    Age
    55
    Posts
    10
    Rep Power
    0

    Re: Digital scroll

    Thanks a lot nike123

    this is a manual for a VRF system, multievaporators, very interesting

    any idea if there is something available also for hydronic, single evaporator systems?

  5. #5
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Digital scroll

    Is it possible to control temperarure and Relative Humidity with only Electronic Expansion Valve.If it is possible, kindly explain how it is achieved.

  6. #6
    Join Date
    Jun 2008
    Location
    Las Vegas
    Age
    64
    Posts
    11
    Rep Power
    0

    Re: Digital scroll

    TO Control RH you lower the capacity to increase run time while keeping the evap under dew point. To Raise RH (provided you have enough moisture input to begin with an empty cooler with no aspirating media would not work or you add humidifier) You Raise Capacity over that neassassary to cool the space to shorten the run time thereby cooling in the shortest possiable time removing as little as possiable moisture.
    IN Meat curing roms we use Freezer coils Wide range TXV's and small misters. the Misters are set at the min Humidity nessassary the heaters are set at the maximum Humdity, and system capacity is designed by load calcs plus 10%, this system is very energy unconscious but it is simple. The electronic TXV would be the best but still would need some form of humidification occationally.

  7. #7
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Digital scroll

    Quote Originally Posted by Sridhar1312 View Post
    Is it possible to control temperarure and Relative Humidity with only Electronic Expansion Valve.If it is possible, kindly explain how it is achieved.
    No, you can not. As Chilly1 says, the only possibility is to lower it until you reach a point above the coils dew point at the set temperature. But the final air water content will depend on other conditions (moisture given off by the product, infiltration conditions, etc)! Only if you have no added moisture you could know final relative humidity. With normal TXVs you cannot do even this but you are not controlling it in the way I understand "controll".

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Digital scroll

    Quote Originally Posted by Camalla View Post
    Hi,
    I'm new in this forum and in this field/market

    has anyone heard about Copeland digital scroll and its performance in hydronic systems (chillers / heat pumps)?

    any idea on how to control it? how would you drive the EXV given the pulsating nature of the compressor?

    thanks fo your help
    Together with the compressor, they deliver also the proper controller for the valve.
    You don't have pulsations with a scroll and you even don't see pulsations with the digital scroll while throttled. The pulsations are flattened out in the evaporator and condenser.
    If you should see pulsations, the you should see those also with the EEV's from Danfoss (AKV's puls/pause principle)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Digital scroll

    Quote Originally Posted by Sridhar1312 View Post
    Is it possible to control temperarure and Relative Humidity with only Electronic Expansion Valve.If it is possible, kindly explain how it is achieved.
    With just an electronic expansion valve, no. But it is part of a system that allows precise temperature and humidity control.
    Basic idea is to modulate system capacity (compressor speed and expansion valve restriction) to regulate amount of cooling and air handler fan speed to optimize the system for dehumidification or cooling. Since A/C systems are more efficient at part load, a smart controller can try to run the compressor at low speeds when possible. The air handler fan runs at lower speeds in relation to compressor capacity for more effective dehumidification.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  10. #10
    urajat's Avatar
    urajat Guest

    Re: Digital scroll

    I know one manufacturer blue star they manufacture VRF system with digital scroll. Humidity is controlled by controlling dt of evaporater and heaters. for humidification humidifier is used.

  11. #11
    Join Date
    Nov 2008
    Location
    Thailand
    Posts
    5
    Rep Power
    0

    Re: Digital scroll

    I heard that, in VRF system, digital scroll is better than inverter in term of dehumidification because of....(I am not quite clear)... Can someone explain in details why?

  12. #12
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: Digital scroll

    We have installed many digital scroll systems and yes it is way better than inverter system in all respects.
    Digital scroll capacity modulation is from 10% to 100% with respective power consumption of 10%-100% also it has very less rather none electronic components compared to inverter system. Inverter cannot run below 40% compared to 10% of digital compressor system. EER of digital scroll is way higher than best japanese inverter in market.
    I have whole presentation in this regard. I can email you if you want. Also click link below

    http://www.digitalscroll.com

    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  13. #13
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: Digital scroll

    Quote Originally Posted by thmech View Post
    I heard that, in VRF system, digital scroll is better than inverter in term of dehumidification because of....(I am not quite clear)... Can someone explain in details why?
    It has low sensible heat ratio (LSHR)that is sole reason of better dehumidification +-2%
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  14. #14
    Join Date
    Nov 2008
    Location
    Thailand
    Posts
    5
    Rep Power
    0

    Re: Digital scroll

    [/quote]

    Quote Originally Posted by abbasi View Post
    It has low sensible heat ratio (LSHR)that is sole reason of better dehumidification +-2%
    I am so busy for while, by the way thank you.


    [quote=abbasi;126939]We have installed many digital scroll systems and yes it is way better than inverter system in all respects.
    Digital scroll capacity modulation is from 10% to 100% with respective power consumption of 10%-100% also it has very less rather none electronic components compared to inverter system. Inverter cannot run below 40% compared to 10% of digital compressor system. EER of digital scroll is way higher than best japanese inverter in market.
    I have whole presentation in this regard. I can email you if you want. Also click link below


    Yes, I am interesting in that presentation so can you mail it to me at kobj03 yahoo mail.

  15. #15
    Join Date
    Oct 2008
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: Digital scroll

    We have installed many digital scroll systems and yes it is way better than inverter system in all respects.
    Digital scroll capacity modulation is from 10% to 100% with respective power consumption of 10%-100% also it has very less rather none electronic components compared to inverter system. Inverter cannot run below 40% compared to 10% of digital compressor system. EER of digital scroll is way higher than best japanese inverter in market.
    I have whole presentation in this regard. I can email you if you want. Also click link below
    Sound good. What application have you used the Digital Scroll system with? What OEMs did you use?

  16. #16
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Digital scroll

    You need to check out the facts yourself.

    From personal experiance & technical manuals to hand i find that the information in the Emerson presentation to be highly misleading. Ofcourse any manufacturer will try to spin information to make there product look like the best product available.

    But the claims about poor performance of VRF systems are completely overstated & mileading when checked against technical data for leading VRF manufacturers.

    If any critical investigation of all digital scroll manufacturers was undertaken & one negative point taken from each & then the accumulation of all those negative points compared to the best VRF system, then the presentation would clearly show that VRF is much better than DS.

    When viewing any manufacturers presentation about the features & advantages of that product you do need to be able to see past the smoke screen & spin & mis information.

    You very often will find the advantages of the product overstated & the disadvantages of the competition overstated & the benifits of the competion not mentioned at all.

  17. #17
    Join Date
    Oct 2008
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: Digital scroll

    It is interesting to find VRF systems being applied where traditional A/C systems have been commonly used in the past. High rise buildings, commercial complex with huge spaces now use VRF systems specially in Asia.

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Digital scroll

    Quote Originally Posted by mekaniko5 View Post
    It is interesting to find VRF systems being applied where traditional A/C systems have been commonly used in the past. High rise buildings, commercial complex with huge spaces now use VRF systems specially in Asia.
    That doesn't mean that VRF is technically better solution than Digital Scroll or water chiller systems.
    Compare that with VHS and BETA video system.
    Beta is much more advanced but VHS is commercially cheaper and simpler to produce. Availability wins over technical excellence when customers are wiling to tolerate that.

  19. #19
    Join Date
    Oct 2008
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: Digital scroll

    That doesn't mean that VRF is technically better solution than Digital Scroll or water chiller systems
    Digital Scroll Compressors are actually being used for VRF System.

    The main difference from other modulated capacity system more commonly named as VRVs is that the motor runs at a fixed speed rather that variable speeds.

Similar Threads

  1. vrv vs digital scroll
    By katyalrk in forum Technical Discussions
    Replies: 16
    Last Post: 16-11-2010, 08:03 PM
  2. copeland digital scroll tech
    By Lc_shi in forum Air Conditioning
    Replies: 6
    Last Post: 27-05-2009, 12:24 AM
  3. use of digital scroll technology
    By katyalrk in forum Technical Discussions
    Replies: 6
    Last Post: 11-11-2008, 02:12 PM
  4. Digital Scroll Technology
    By Dan in forum New Technologies
    Replies: 7
    Last Post: 17-06-2008, 08:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •