Thread: how can i calculate superheat
20-04-2008, 12:07 PM #1
how can i calculate superheat from the evaps to the comps if i have no thermosat near the evaps , for any help thanks grant
20-04-2008, 01:03 PM #2
Re: how can i calculate superheat
Please use the Search function, there must be at least 10 recent posts about this...
20-04-2008, 01:09 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
You mean non-useful superheat? Simply by measuring pipe temperature at evaporator outlet by thermometer and after that by measuring pipe temperature at least 10" (but not much further) from compressor by thermometer.
Then subtract lower value from higher and there is your non-useful superheat.
More about that:
http://www.refrigeration-engineer.co...ead.php?t=1124
18-05-2008, 04:35 AM #4
yeah .. i agree that i really the helps from other gadgets.
that why i always insist the preparation of
1] IR temp gun;
2] pressure gage;
3] glass bulb thermometer;
4] etc.
when supheat or expansion valve has to be adjusted/tuned.
hope that helps.
Hendry, on wesak day holiday.Hendry
"What uncertainty means to you, and you only?"
01-06-2008, 08:46 AM #5
thanks guys , ive got it
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
TEV superheat setting and low temperatures
By DaBit in forum FundamentalsReplies: 11Last Post: 01-03-2010, 03:11 AM -
discharge superheat
By philjd26 in forum Trouble ShootingReplies: 8Last Post: 09-01-2008, 08:48 AM -
Superheat
By shogun7 in forum FundamentalsReplies: 24Last Post: 23-08-2004, 05:54 PM -
How do you calculate Superheat?
By zolar1 in forum TrainingReplies: 39Last Post: 10-05-2002, 02:37 AM