18-04-2008, 11:08 PM #1
Vertical Insulation freezer panels
Hi All,
What is the maximum unaided support heights for 150mm and 200mm thick Polyurethane insulated panel (for a freezer application).
The freezer I have is 13meter clear internal height.
19-04-2008, 06:59 AM #2
Re: Vertical Insulation freezer panels
If you are using lockable panels, you can install them without any support. But if those are panels without locks. you shall need atleast Two supports in vertical for the wall panels. There are various ways of supporting them. May be I can send you the drawing for that on your mail.
19-04-2008, 10:24 AM #3
Hi samian,
a general guide will be -
150mm panel max vertical height -30 deg application 10 meters.
200mm panek max vertical height -30 deg application 12.8 meters.
although it is always best to consult with the panel manufacturer.
Billy Ray
20-04-2008, 07:53 AM #4
I am making cold rooms up to 14 m H freezer with out any support and no problem with Camlock system
20-04-2008, 08:50 AM #5
Yes we too have similar heights with lockable panels.
But with no cam locks, we are providing supports for the wall panels.
23-04-2008, 12:28 AM #6
Dear friends
The vertical supports also depend upon the panels location.
If the panel is faced to outside you should consider the wind force
Gwapa
07-05-2008, 05:03 PM #7
Dear friend
The floor will also affect the vertical support. If the cold room is not properly insulated on the floor, the floor will give way. Due to super dry concrete (that is provided if it is concrete used)
Need help quick with walk-in freezer issues!
By hysiderafter in forum CommercialReplies: 5Last Post: 12-12-2007, 01:57 AM -
freezer insulation
By jayjay in forum CommercialReplies: 48Last Post: 21-12-2006, 06:02 AM -
insulation panels
By tonto33 in forum CommercialReplies: 0Last Post: 16-10-2006, 02:16 PM -
New Freezer Room Panels
By Abe in forum Legal-Business-MarketingReplies: 7Last Post: 04-05-2005, 09:43 AM -
Freezer Room Panels
By Feeze in forum Technical DiscussionsReplies: 10Last Post: 22-04-2005, 05:58 AM