    Industrial water chiller



    I will appreciate any friend to tip me or suggest what to be done to design the industrial water chiller, for tank capacity 5000gallon, ambient temp.45deg.C and design temp will be 20deg.C , I would like to know if cooling load estimation can be done through cold storage design software or there is special software related to water cooling load?, I like to share experience of friend on this , as it is the first time this come to me as challenge and i preffer to have great idea instead of biten about the bush, any idea is welcome,and I am appreciating software and other tips , thanks in advance



  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Industrial water chiller

    You shall need Temp difference i.e. cooling water from Which temp to desired temp. If the entire water is to be cooled in the tank, what is te time for cooling from its high temp to low temp. Then the calculations are very easy

  3. #3
    Join Date
    Dec 2007
    Location
    Kuwait
    Posts
    15
    Rep Power
    0

    Re: Industrial water chiller

    [quote=smpsmp45;103167] , thanks smpsmp45, the temperature difference will be 25deg.c, cooling time average will be 6hrs,

    I will be greateful to have your experience shared and your special advice is highly appreciated.
    Ibraheem

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Industrial water chiller

    The heat laod shall be

    GPM x Delta T / 24
    (5000 / 6 /60) x 25 / 24 = 14.6 TR

    But how does the water come to the chiller. You shall need a scheme to cool that water with a delta T of max 10 Deg F ( Or a Plate Heat exchanger to achieve that high Delta T across the evaporator

  5. #5
    Join Date
    Dec 2007
    Location
    Kuwait
    Posts
    15
    Rep Power
    0

    Re: Industrial water chiller

    Hi, my friend, a lot of thanks to you, I had simillar case this week and even bigger system, as I was given flow rate of water 70liter/sec, this seem too big to me , as they have water tank of volume capacity of 36000liter,delta T will be 17 Deg C , this chiller water inlet will be 45Deg and out let temp 28 Deg C , I am confusing should I use the given flowrate to calculate the cooling capacity or I have to deal with tank capacity only to select the chiller capacity? I would like to share your rich experience on this issues as Iam dealing with water chiller for the first time, this system water wil be coming from even cooling tower before entering to chiller at temp.45Deg C.

Similar Threads

  1. water chiller question
    By chillman in forum Technical Speculations
    Replies: 2
    Last Post: 12-03-2008, 10:21 PM
  2. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  3. Water chiller help
    By ultralo1 in forum Trouble Shooting
    Replies: 6
    Last Post: 12-05-2007, 11:52 AM
  4. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 07:14 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •