Results 1 to 7 of 7
Thread: mitsubishi 6607 error
-
18-04-2008, 10:27 AM #1
mitsubishi 6607 error
hi,
have to tackle this error tommorrow and dont really have much experience with mitsu, the manual has a list amile long with possibilities.... can anyone give me the common causes for this alarm, what should i lookj out for...?
rgrds
-
18-04-2008, 10:35 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: mitsubishi 6607 error
There are two Mitsubishi (Electric and Heavy Industries)
and lot of models. What is your case?
-
18-04-2008, 11:11 AM #3
Re: mitsubishi 6607 error
From the error code I assume it's an Electric.
City Multi
Communication error - No ACK return the MNET cannot communicate with the address given, check for 30VDC at TB5 on that address possible address board error
Mr Slim R410A
Non defined error code, reset outdoor power, non power inverter outdoor fitted, wrong remote controller, indoor or outdoor board faulty
Mr Slim R410A
NO ACK signal check A-Mnet wiring, range of transmission wiring exceeded, faulty A-Mnet converter
Mr Slim R407c
Non defined error code, reset outdoor power, non power inverter outdoor fitted, wrong remote controller, indoor or outdoor board faulty
Mr Slim R407c
NO ACK signal check A-Mnet wiring, range of transmission wiring exceeded, faulty A-Mnet converterLast edited by The Viking; 18-04-2008 at 11:13 AM.
-
18-04-2008, 03:59 PM #4
-
18-04-2008, 06:39 PM #5
Re: mitsubishi 6607 error
City Multi VRF system ?
If the site has a G50 or Mj103 central controller it will report 6607 for the outdoor unit & all indoor units connected to it when the 3ph power is lost at the outdoor unit.
This is because the 30v d/c M-net communication voltage is generated at a transformer in the outdoor unit. Then every unit & local remote controller connected to that outdoor unit superimpose communication data onto the 30v d/c.
So in this case if no power to outdoor unit then the centralised controller cannot get any reply from any unit connected to that outdoor unit & will report 6607 fault for all the units.
Provided all units are still connected to the M-net 30v d/c & have not changed address settings then they can all communicate. Even if 240v power is switched off at any indoor units they can all still communicate on the M-net.
This is completely different to most other VRF/VRV systems which operate on 5 to 12v d/c & will stop on a comms fault if 240v switched off at any indoor unit.
Ask for the O&M manual & hopefully there will be an as installed drawing showing the M-net address for all the units.
Start at the outdoor unit confirm address & 30v d/c then work arround the system to confirm address of all units & 30v d/c.
As you have noted 6607 covers a multitude of sins but with the fault code is also the address which has the problem. Because the address setting is in 99% cases manually set on every unit in most cases just need to find the unit which is when the as installed drawings come in real handy.
Good luck
-
18-04-2008, 08:19 PM #6
Re: mitsubishi 6607 error
hi
thermatech- have touch screen central control think its the Mj103, i know that there is juice at the out door unit and have only seen the error been displayed on the c/c.... the other thing is i ran all associated indoors to this unit, and the outdoor is does feck all.... any ideas?, i will confirm all address and comm dcv tommorrow...thanks for the reply therma have a idea of approach..thanks again lads..
rgrds phil
-
21-04-2008, 02:42 AM #7
Re: mitsubishi 6607 error
I took a quick look at the tech manual for a Mitsubishi PUHY c/u and it looks like a communication error with lots of choices for the error. I have never had that error so I wish you luck in finding it. If you don't have the tech manual for the system you are working on you can probably find it here in pdf form.
Copy & paste since this website won't let me post URL's
mrslim.com/customerCare/resources.asp
I would be curious to hear what the problem what the problem was.
Similar Threads
-
shining fault codes
By al in forum Air ConditioningReplies: 3Last Post: 17-07-2010, 08:34 AM -
Mitsubishi Heavy Error Codes
By Peter_1 in forum Air ConditioningReplies: 2Last Post: 30-11-2007, 08:38 AM -
Mitsubishi compressor lock
By marc5180 in forum Air ConditioningReplies: 29Last Post: 08-10-2007, 05:48 PM -
Angelopo Sm2l Error E2 Please Info About This Error
By CHARLIEZOLO in forum CommercialReplies: 4Last Post: 23-12-2005, 09:00 PM -
Angelopo Sm2l Error E2 Please Info About This Error
By CHARLIEZOLO in forum CommercialReplies: 0Last Post: 22-12-2005, 03:47 AM