Results 1 to 3 of 3
  1. #1
    strumbeat's Avatar
    strumbeat Guest

    W3000 pCO2 or pCO3 & Integration



    Hi from South Africa

    We are looking at Integrating 4 Turbo Core Climaveneta chillers which use the W3000 Controls to our Johnson Controls BMS

    We have mapping tables for the pCO2 controller but i think the W3000 is a pCO3 ??

    Any advice ?

    Any Johnson fundi's out there ?

    regards

    PETE



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: W3000 pCO2 or pCO3 & Integration

    If you think that W3000 is Carel pCO3 then here are the data for pCO3:
    http://tinyurl.com/3e9m5b

  3. #3
    Join Date
    Sep 2003
    Location
    sout east uk
    Age
    45
    Posts
    15
    Rep Power
    0

    Re: W3000 pCO2 or pCO3 & Integration

    The W3000 is only PCO3 hardware. It has bespoke climaveneta software in it so the carel manual will not work.

    You can use with the folowing BMS via a serial card and the supervisor network.

    MODBUS, TREND, LONWORKS, BACNET,

    I have the manual but cant't upload it because it is 671.9 KB.