Results 1 to 3 of 3
Thread: W3000 pCO2 or pCO3 & Integration
-
17-04-2008, 09:59 AM #1
W3000 pCO2 or pCO3 & Integration
Hi from South Africa
We are looking at Integrating 4 Turbo Core Climaveneta chillers which use the W3000 Controls to our Johnson Controls BMS
We have mapping tables for the pCO2 controller but i think the W3000 is a pCO3 ??
Any advice ?
Any Johnson fundi's out there ?
regards
PETE
-
17-04-2008, 11:31 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: W3000 pCO2 or pCO3 & Integration
If you think that W3000 is Carel pCO3 then here are the data for pCO3:
http://tinyurl.com/3e9m5b
-
22-11-2008, 02:39 PM #3
Re: W3000 pCO2 or pCO3 & Integration
The W3000 is only PCO3 hardware. It has bespoke climaveneta software in it so the carel manual will not work.
You can use with the folowing BMS via a serial card and the supervisor network.
MODBUS, TREND, LONWORKS, BACNET,
I have the manual but cant't upload it because it is 671.9 KB.