    Can anybody please tell me about the various tests conducted on the chilled water FCU's
    Also How these tests are conducted.



  2. #2
    Join Date
    Jun 2006
    Location
    India
    Age
    63
    Posts
    28
    Rep Power
    0

    Re: Chilled Water FCU Tests

    Dear Munesh,
    I think you would like to acertain the capacity of the FCU for air conditioning application.

    FCUs are normally cross flow type heat exchangers and you can simply define the capacity by heat balance equation.

    1. Water Side: Q(W)=Mass Flow Rate of water X Sp.Heat X Temp. Diff. of water at inlet & Outlet

    2. Air Side: Q(A)= Mass Flow Rate of Air X Enthalpy Diff. of air at inlet & outlet.

    3. See that Q(W) equals Q(A) for perfect design.

  3. #3
    Join Date
    Sep 2006
    Location
    india
    Age
    47
    Posts
    51
    Rep Power
    18

    Re: Chilled Water FCU Tests

    Thanks for your reply. I came to know of various tests but need to ascertain how these are carried out.
    I) Air Volume Test
    II) Cooling & Heating Capacity Test
    III) Condensation Test
    IV) Dielectric Test
    V) Insulation Resistance Test
    VI) Sound Level Test
    VII) Vibration Test
    VIII) Protection Devices test

    Can anyone help me with how these can be conducted, Any special equipment or testing device required etc.

  4. #4
    Join Date
    Sep 2006
    Location
    india
    Age
    47
    Posts
    51
    Rep Power
    18

    Re: Chilled Water FCU Tests

    I could Lay hands on
    Dielectric Test: Measures Current Leak when the phase and neutral are short circuited
    Insulation test: Measures resistance wheh the phase and neutral are short circuited. Measured with a megometer. Measurements in Ohmic values.

    Any additions

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled Water FCU Tests

    I) Air Volume Test

    Test rig comprising ductwork to simulate actual duct resistance. Airflow measured via pitot-static tube and manometer.

    II) Cooling & Heating Capacity Test

    Lots of thermometers ?

    III) Condensation Test

    Stop watch, liquid measuring scale, psychrometric chart.

    IV) Dielectric Test
    V) Insulation Resistance Test

    VI) Sound Level Test

    Sound level meter and testing chamber.

    VII) Vibration Test

    Test bed and vibration analysis meter.

    VIII) Protection Devices test

    What sort of devices are you meaning?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Sep 2006
    Location
    india
    Age
    47
    Posts
    51
    Rep Power
    18

    Re: Chilled Water FCU Tests

    thanks a Lot Brian & Varde

Similar Threads

  1. Energy saving in Chilled water system
    By psrao in forum Tools and Calculators
    Replies: 5
    Last Post: 15-01-2008, 06:54 PM
  2. Honeywell chilled water temperature controller
    By Cofreth in forum Technical Discussions
    Replies: 4
    Last Post: 07-09-2007, 06:32 PM
  3. Chilled water treatment
    By benj in forum Commercial
    Replies: 1
    Last Post: 04-09-2007, 04:44 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Replies: 1
    Last Post: 31-07-2002, 08:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •