    Sep 2006
    india
    47
    Chilled Water FCU Tests
    Can anybody please tell me about the various tests conducted on the chilled water FCU's
    Also How these tests are conducted.
    Jun 2006
    India
    63
    28
    Re: Chilled Water FCU Tests
    Dear Munesh,
    I think you would like to acertain the capacity of the FCU for air conditioning application.
    FCUs are normally cross flow type heat exchangers and you can simply define the capacity by heat balance equation.
    1. Water Side: Q(W)=Mass Flow Rate of water X Sp.Heat X Temp. Diff. of water at inlet & Outlet
    2. Air Side: Q(A)= Mass Flow Rate of Air X Enthalpy Diff. of air at inlet & outlet.
    3. See that Q(W) equals Q(A) for perfect design.
    Sep 2006
    india
    47
    Thanks for your reply. I came to know of various tests but need to ascertain how these are carried out.
    I) Air Volume Test
    II) Cooling & Heating Capacity Test
    III) Condensation Test
    IV) Dielectric Test
    V) Insulation Resistance Test
    VI) Sound Level Test
    VII) Vibration Test
    VIII) Protection Devices test
    Can anyone help me with how these can be conducted, Any special equipment or testing device required etc.
    Sep 2006
    india
    47
    I could Lay hands on
    Dielectric Test: Measures Current Leak when the phase and neutral are short circuited
    Insulation test: Measures resistance wheh the phase and neutral are short circuited. Measured with a megometer. Measurements in Ohmic values.
    Any additions
    I) Air Volume Test
    Test rig comprising ductwork to simulate actual duct resistance. Airflow measured via pitot-static tube and manometer.
    Lots of thermometers ?
    Stop watch, liquid measuring scale, psychrometric chart.
    IV) Dielectric Test
    Sound level meter and testing chamber.
    VII) Vibration Test
    Test bed and vibration analysis meter.
    What sort of devices are you meaning?
    Sep 2006
    india
    47
    thanks a Lot Brian & Varde
  1. Energy saving in Chilled water system
    By psrao in forum Tools and Calculators
    Last Post: 15-01-2008, 06:54 PM
  2. Honeywell chilled water temperature controller
    By Cofreth in forum Technical Discussions
    Last Post: 07-09-2007, 06:32 PM
  3. Chilled water treatment
    By benj in forum Commercial
    Last Post: 04-09-2007, 04:44 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Last Post: 31-07-2002, 08:25 PM