Results 1 to 11 of 11
Thread: NH3 pump or DX
    May 2006
    India
    82
    1,013
    NH3 pump or DX
    I would like to know for a small unit of say 60 kw for maintaining a Room Temperature of - 32 oC, with Ammonia as a refrigerant, is it advisable to have a pump system or a DX system.
    Thanks.
    Aug 2005
    5,302
    Re: NH3 pump or DX
    Samarjit,
    You need to see if the TXV and evaporator manufacturers will provide equipment suitable for this cold of a temperature using DX on ammonia.
    DX control with ammonia at low temperatures can be a big problem.
    The simplest way to do this if you only have one or two evaporators is to use flooded coils on ammonia. If you have many evaporators then a liquid overfeed system (pumped) can be more cost effective than flooded.
    I do not like DX on ammonia for anything, but that is just my opinion.
    May 2006
    India
    82
    1,013
    Re: NH3 pump or DX
    It is just one room meant to harden the ice cream. The total heat load comes to about 56 kw. On the bsais of this I selected the compressor. Now as far as I know that with ammonia it is not possible to attain this temperature without an additional booster compressor. That means the cost goes up as well the system becomes more complicated. I am thinking of using 4 compressors each of 14 kw at - 38 oC Te and 20 oC Cond. For the condensing temperature I propose to use chilled water at 7 oC inlet through the Shell & Tube Condenser. For this I will definately have to use an additional smaller capacity compressor. The Compressor I propose to use is open type Bock.
    Please could you guide me if I am wrong. You know Mike I am not much aquainted with ammonia.
    The evaporator manufacturer has offered both the DX and the Pump system. I very well remember that some where in the forum, Mike had earlier discouraged me or some one from using DX for NH3.
    Jan 2006
    Valrico, Florida
    509
    Re: NH3 pump or DX
    I don't like DX either, and was just looking at it cost wise, what kind of problems have you experienced with DX at that temp?
    May 2006
    India
    82
    1,013
    Re: NH3 pump or DX
    I guess using a DX system would not be proper. So it has to be a pump system. Either I shall have two compressors installed or 4 each with its individual Evaporators. But considering the cost, I feel that I shall prefer to install two nos of compressors and each connected to two coils. Before I seek further opinion I would like to know if my thoughts are correct or not. For two units I shall go in for Vilter as the same is being manufactured in India with Frick.
    Aug 2005
    5,302
    Re: NH3 pump or DX
    Samarjit,
    You also have to think about defrosts too. If you have 4 evaporators, one of the four should only be in defrost at a single time. Then the other 3 coils would be cooling the room and providing heat for the hot gas defrost cycle.
    For a load of ~60 kW you may be able to use only three compressors. One low-stage compressor, 1 hi-stage compressor, and 1 for a spare compressor (piped in to allow changing for either of the compressors).
    May 2006
    India
    82
    1,013
    Re: NH3 pump or DX
    Could I have a single line drawing of the system with the equipments .
    May 2006
    India
    82
    1,013
    Re: NH3 pump or DX
    Does Vilter have a compound reciprocating compressor suitable for Ammonia.
    Jul 2006
    74
    865
    26
    Re: NH3 pump or DX
    Quote Originally Posted by Samarjit Sen View Post
    Yes they do. Pipe to an Intercooler and you are done. Very good machines.
    Jun 2006
    jiansu
    38
    Re: NH3 pump or DX
    Why not use a frone DX system, it is very simple.
    R404A is a good refrigerant.
    May 2006
    India
    82
    1,013
    Re: NH3 pump or DX
    Yes ***** wuld be much better. We have been so far using ***** 22 refrigerant for our projects for - 35 oC and even for Rm Temo. at - 40 oC. In the same site we have installed three units with 22. The client now wants with Ammonia.
    As we have not done much with NH3, I am seeking the assistance of you members to guide me.
  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Last Post: 20-05-2011, 02:18 AM
  2. Daikin lift pump
    By Slim R410a in forum Air Conditioning
    Last Post: 13-07-2009, 11:12 PM
  3. Help with condensor pump
    By Bakerbj in forum Air Conditioning
    Last Post: 14-06-2009, 12:39 AM
  4. frostles heat pump
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Last Post: 29-01-2008, 09:27 PM