    NH3 pump or DX



    I would like to know for a small unit of say 60 kw for maintaining a Room Temperature of - 32 oC, with Ammonia as a refrigerant, is it advisable to have a pump system or a DX system.

    Thanks.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: NH3 pump or DX

    Samarjit,

    You need to see if the TXV and evaporator manufacturers will provide equipment suitable for this cold of a temperature using DX on ammonia.

    DX control with ammonia at low temperatures can be a big problem.

    The simplest way to do this if you only have one or two evaporators is to use flooded coils on ammonia. If you have many evaporators then a liquid overfeed system (pumped) can be more cost effective than flooded.

    I do not like DX on ammonia for anything, but that is just my opinion.
    If all else fails, ask for help.


  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: NH3 pump or DX

    It is just one room meant to harden the ice cream. The total heat load comes to about 56 kw. On the bsais of this I selected the compressor. Now as far as I know that with ammonia it is not possible to attain this temperature without an additional booster compressor. That means the cost goes up as well the system becomes more complicated. I am thinking of using 4 compressors each of 14 kw at - 38 oC Te and 20 oC Cond. For the condensing temperature I propose to use chilled water at 7 oC inlet through the Shell & Tube Condenser. For this I will definately have to use an additional smaller capacity compressor. The Compressor I propose to use is open type Bock.

    Please could you guide me if I am wrong. You know Mike I am not much aquainted with ammonia.

    The evaporator manufacturer has offered both the DX and the Pump system. I very well remember that some where in the forum, Mike had earlier discouraged me or some one from using DX for NH3.

  4. #4
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: NH3 pump or DX

    I don't like DX either, and was just looking at it cost wise, what kind of problems have you experienced with DX at that temp?

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: NH3 pump or DX

    I guess using a DX system would not be proper. So it has to be a pump system. Either I shall have two compressors installed or 4 each with its individual Evaporators. But considering the cost, I feel that I shall prefer to install two nos of compressors and each connected to two coils. Before I seek further opinion I would like to know if my thoughts are correct or not. For two units I shall go in for Vilter as the same is being manufactured in India with Frick.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: NH3 pump or DX

    Samarjit,

    You also have to think about defrosts too. If you have 4 evaporators, one of the four should only be in defrost at a single time. Then the other 3 coils would be cooling the room and providing heat for the hot gas defrost cycle.

    For a load of ~60 kW you may be able to use only three compressors. One low-stage compressor, 1 hi-stage compressor, and 1 for a spare compressor (piped in to allow changing for either of the compressors).
    If all else fails, ask for help.


  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: NH3 pump or DX

    Could I have a single line drawing of the system with the equipments .

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: NH3 pump or DX

    Does Vilter have a compound reciprocating compressor suitable for Ammonia.

  9. #9
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: NH3 pump or DX

    Quote Originally Posted by Samarjit Sen View Post
    Does Vilter have a compound reciprocating compressor suitable for Ammonia.
    Yes they do. Pipe to an Intercooler and you are done. Very good machines.

  10. #10
    Join Date
    Jun 2006
    Location
    jiansu
    Posts
    38
    Rep Power
    0

    Re: NH3 pump or DX

    Why not use a frone DX system, it is very simple.
    R404A is a good refrigerant.

  11. #11
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: NH3 pump or DX

    Yes ***** wuld be much better. We have been so far using ***** 22 refrigerant for our projects for - 35 oC and even for Rm Temo. at - 40 oC. In the same site we have installed three units with 22. The client now wants with Ammonia.

    As we have not done much with NH3, I am seeking the assistance of you members to guide me.

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Daikin lift pump
    By Slim R410a in forum Air Conditioning
    Replies: 10
    Last Post: 13-07-2009, 11:12 PM
  3. Help with condensor pump
    By Bakerbj in forum Air Conditioning
    Replies: 23
    Last Post: 14-06-2009, 12:39 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •