    Feb 2008
    New Zealand
    12
    yet another oil problem
    Hi all,
    Got a Frick ammonia compressor, zero oil pressure, done the obvious new filtrers, cleaned strainers.
    The oil at the inlet of the oil primer pump is white froth so suspect pump not picking up.
    Can not having oil heaters functioning cause this, given machine only shut down a few hours or most likely water contamination fron PHE oil cooler?
    appreciate your thoughts , comp had been running sweet for weeks
    Mar 2008
    Dallas, Oregon
    72
    Re: yet another oil problem
    I hate to ask the most obvious question of all, but is it possible that your compressor is just low on oil?
    I have an old Frick rotary booster that causes me oil problems if the oil temperature becomes too low. At low temperature the oil foams badly and will carry over into my flash cooler, leaving the compressor low on oil. I might add that it does not take operating my compressor very long at low temperature to develop this problem.
    Feb 2008
    New Zealand
    12
    Thanks mate,
    plenty of oil but it appears that the heaters are not working so maybe that is causing the oil temp to be come to low, the machine seperator was cold when I went to start it so will work on that today
    Aug 2005
    5,302
    If the oil separator is ambient temperature when you start it up, then you probably have issues with the sump heaters.
    If the oil separator is colder than ambient temperature you could have liquid refrigerant sitting in the sump. The oil sump heaters are not sized to burn off the ammonia in this case. If this happened, then you probably have issues with flood back.
    Feb 2008
    New Zealand
    12
    Thanks guys, found the problem, much easier sorting out problems during "normal" working hours instead of 12.30am when I should have been asleep!
    Oil pump knackered, rotors jammed and broke the motor spline, motor was running but pump wasn't
    Jul 2006
    74
    865
    26
    Sometimes it is the simplest of problems that takes the most work to find.
    Stuff happens
    Aug 2005
    5,302
    And another important lesson to be learned...
    Always check the easy things first.
  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Last Post: 27-10-2010, 05:21 PM
  2. what's the problem
    By botrous in forum Air Conditioning
    Last Post: 22-06-2008, 02:54 AM
  3. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Last Post: 07-03-2008, 05:13 AM
  4. Oil carry over Problem in Refrigeration Unit
    By imranmd in forum Industrial
    Last Post: 27-08-2007, 03:09 PM
  5. LG 10.5 kw cassette timer problem
    By Andy W in forum Air Conditioning
    Last Post: 25-06-2005, 07:09 PM