    No defrost on Daikin



    Hi Guys. I normally work on commercial refrigeration plants, but was asked to look at a Daikin heat pump because it kept on icing up (outdoor coil) on heat mode. I reclaimed and recharged the system so the critical charge is good. The sensors (coil and ambient) test out ok.
    The whole coil is icing evenly except for the bottom 200mm where their is no ice.
    Could this be a sign of a blocked capillary which is not cooling the defrost sensor to bring in the defrost?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: No defrost on Daikin

    Did you checked air quantity at outdoor unit when it is normal operating mode (heating)?

    This is how heat pump looks when there is no sufficient air flow.
    Last edited by nike123; 11-04-2008 at 10:33 AM.

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: No defrost on Daikin

    Quote Originally Posted by Drew View Post
    Hi Guys. I normally work on commercial refrigeration plants, but was asked to look at a Daikin heat pump because it kept on icing up (outdoor coil) on heat mode. I reclaimed and recharged the system so the critical charge is good. The sensors (coil and ambient) test out ok.
    The whole coil is icing evenly except for the bottom 200mm where their is no ice.
    Could this be a sign of a blocked capillary which is not cooling the defrost sensor to bring in the defrost?
    Could be, the coil sensor is normally down the bottom of the coil, and systems usually start frosting at the bottom. Did you manage to get a look at the distributor to see if it's unevenly iced up or get pipe temperatures.
    Is this system a TX valve or electronic valve with 1/4" tube distributors, or no valves and just small capilaries from the liquid line?
    I'm not a daikin expert, but usually posting the model number will get more useful advice from people here.

    How big is this coil, is 200mm 25%, 5% or what? Is it a single sided coil, or wrap around etc and where else is iced up/not iced up (ie other coils from the same distributer feed, suction line etc)

    edit: Could you remove the coil thermistor from the bottom, cable tie it to a frosted up section of coil, cover it with cork tape and verify auto defrost works? If the rest of the coil is icing up then this should test that the thermistor and PCB ae good.
    Last edited by paul_h; 11-04-2008 at 10:49 AM.

  4. #4
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    218
    Rep Power
    17

    Re: No defrost on Daikin

    It has proven to be a blocked capillary.
    Thanks all.

  5. #5
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    218
    Rep Power
    17

    Re: No defrost on Daikin

    Thanks paul. That is how i did prove the fault . Once the client noticed that it wasnt icing up on cold nights anymore we knew the system was defrosting ok and we then found the blocked capillary.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 05:25 PM
  3. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 09:22 AM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 07:25 PM
  5. Hot gas defrost vs Electric defrost
    By herdian in forum Industrial
    Replies: 19
    Last Post: 13-08-2007, 11:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •