    There is a dunham-bush 200RT screw chiller. the owner said someone set a time lock in the microcomputer control system, so the machine can't startup again, though it ran well in past weeks.

    I have never worked on dunham-bush, so know nothing about it's control system. does it really have a time lock?



  2. #2
    calders's Avatar
    calders Guest
    hi lin
    all dunham bush chillers i have worked on have a 10 minute stop start delay. beit PCX or PC what ever. most large motor manufactures say no more than 4 starts an hour.
    also all the D&B i have seen hare a cam timer which is easy to wind on so be carefull but at the end of the day it is up to you
    regards calders

  3. #3
    Join Date
    Jul 2001
    Location
    Fuzhou, China
    Age
    50
    Posts
    35
    Rep Power
    0
    does it have holiday setting? I cann't find info. about it at the chinese manual.

  4. #4
    Join Date
    Aug 2001
    Location
    Havant, Hampshire, UK
    Posts
    12
    Rep Power
    0
    It does have a Holiday setting in one of the sub menus, but these are rarely used. However go into the Holiday menu and remove any settings to see if the machine will start. Also have you checked in the Alarms list to see if you have any current alarms.

  5. #5
    Join Date
    Jul 2001
    Location
    Fuzhou, China
    Age
    50
    Posts
    35
    Rep Power
    0
    D.Evans,
    thank reply. There isn't any alarm active. It has simple guide for schedule setting in manual, but no holiday. I cann't do anything more without enough info.

  6. #6
    Join Date
    Aug 2001
    Location
    Havant, Hampshire, UK
    Posts
    12
    Rep Power
    0
    Look in the Digital Menu to see if flow switch and unit control inputs say ON . If one of those is OFF the unit will not start.

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. Dunham Bush
    By frank in forum Air Conditioning
    Replies: 9
    Last Post: 03-09-2005, 05:38 PM
  3. Dunham Bush Chillers
    By frank in forum Air Conditioning
    Replies: 14
    Last Post: 11-08-2002, 12:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •