    absorption chiller



    Hi guys lloking for some advice to recommision a large Thermax absorption chiller.I winterised it last year by leaving it with a standing pressure of 3 psi of OFN.
    As I understand it I release the OFN and vac out for approx 48 hours and then let the plant engineers introduce the water.Hope this makes sense.
    All advice welcome



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: absorption chiller

    ???
    I must admit that I'm at a loss here,

    Are you talking about the refrigerant /ammonia side or the chilled water side of things?

  3. #3
    Join Date
    Feb 2008
    Location
    uk
    Posts
    7
    Rep Power
    0

    Re: absorption chiller

    I believe this chiller is hot water driven and the "refrigerant" is the water.Hope this helps.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: absorption chiller

    Hi Toolman

    Has the machine kept the pressure over the winter? If not the bursting disc may have been breached by the pressure.
    Did you measure the amount of pure deairated water you took out of the machine?

    You can't just vacuum for 48 hours and hope that the internal vacuum will be satisfactory. You must have a Torr Gauge fitted and achieve at least 6 Torr which holds steady for 24 hours.

    After you charge the pure deairated water, keep and eye on the vacuum level for the first few weeks, you will find that you need to purge more often

  5. #5
    Join Date
    Apr 2008
    Location
    east london uk
    Posts
    9
    Rep Power
    0

    Re: absorption chiller

    hi torrman, i think you are talking about a single effect chiller using steam or hot water.i note the post by the moderator and he is right .
    has all the water been taken out of the machine? if so then it is important to know the exact quantity as it determines the dilution of libr just before it tends to crystalise.
    i presume the machine has its own evacuation system and it is on all the time the machine is running.
    if an external vac pump is used then it is better to put in the water charge while pulling the vacuum as there will be dissolved air coming out of the water.
    if a high vacuum is acchieved before starting then the plant will run trouble free.
    hope this helps.
    Last edited by swaminathan van; 08-04-2008 at 10:51 AM. Reason: spelling

  6. #6
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: absorption chiller

    Why would you shut the machine down this way? I have never heard of this being done like that.

  7. #7
    absorptionkid's Avatar
    absorptionkid Guest

    Re: absorption chiller

    Hi all,

    Has anyone done it by nitrogen pressurizing @ 0.2 barg before? Maybe not worth for just winter... Just wanted to know some opinions about this...

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  3. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  4. Absorption Chiller
    By frank in forum Air Conditioning
    Replies: 47
    Last Post: 06-08-2010, 08:15 PM
  5. Absorption chiller in winter
    By igorb73 in forum Technical Discussions
    Replies: 2
    Last Post: 16-03-2007, 08:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •