    Mits. SRK 25 ZC-S Fault



    I have a customer with a Mits unit that is faulty. I have visited the customer but found the unit running fine. The usual thing when I am not there is plays up again. Apparently the RUN light flashes twice,Then it may shut down , but not allways. Any ideas? The unit is 5-6 years old and given no prob. before. Any fault codes that I find on the forum don't seem to include this fault. It may be that the customer is miss reading the flashes/lamp readings.



  2. #2
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Mits. SRK 25 ZC-S Fault

    If the timer lamp is on and the run lamp flashes twice - room temp sensor error.
    If the run lamp keeps flashing and the timer lamp flashes twice - outdoor heat exchanger liquid pipe sensor error.
    If the run lamp flashes twice and timer lamp flashes twice - compressor rotor lock - bad news.

    Andy

Similar Threads

  1. vrv3 au fault
    By transit 1 in forum Air Conditioning
    Replies: 6
    Last Post: 04-11-2010, 10:19 PM
  2. Mitsubishi 1500 fault code fault
    By pie man in forum Air Conditioning
    Replies: 9
    Last Post: 06-05-2010, 09:30 PM
  3. Supra common fault - usually misdiagnosed.
    By carrier_trained in forum Transport
    Replies: 3
    Last Post: 15-04-2010, 08:56 PM
  4. mits elect split fault
    By paul_h in forum Air Conditioning
    Replies: 7
    Last Post: 27-01-2009, 11:24 PM
  5. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •