    Evacuation Procedures



    Hi everyone,
    Im looking for advice for evacuation procedures for long piping runs on large commercial ductless equipment. Sizes of system range from 3 ton- 24 ton. I need all the information I can get. My background is in small equipment. I want my first experience of installation to go smooth. Thanks for any input you guys can give me.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Evacuation Procedures

    Try searching this site for some of the many discussions on evacuation procedures.

    Here's one to start with..

    http://www.refrigeration-engineer.co...ght=evacuation

    Basically a proper triple evacuation will get you off to a good start, exactly like your present method of working, we hope
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2006
    Location
    Sterling, IL
    Age
    76
    Posts
    13
    Rep Power
    0

    Re: Evacuation Procedures

    Use two vacuum pumps. One at each end of the system. Might make the evacuation go faster.

  4. #4
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: Evacuation Procedures

    I agree with the triple evacuation. I also use the 1.5-2.0 psi OFN flow while brazing. I ve heard some discussion regarding making it faster in regards to gauge hoses being up-sized, schraders being removed. Any other tips you guys could give woulld help. Desired micron level? Ive been told 500 microns. Do you guys do a standing pressure test? Does it need to hold overnight? Thanks for the input!

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Evacuation Procedures

    Quote Originally Posted by Husky250 View Post
    I agree with the triple evacuation. I also use the 1.5-2.0 psi OFN flow while brazing. I ve heard some discussion regarding making it faster in regards to gauge hoses being up-sized, schraders being removed. Any other tips you guys could give woulld help. Desired micron level? Ive been told 500 microns. Do you guys do a standing pressure test? Does it need to hold overnight? Thanks for the input!

    Sounds like you got it about right to me.
    If the pipes a purged with OFN and then a good tripple vac carried out you won't go far wrong.
    As for the depth of vac I would aim for about 15torr first 10 torr second 4 torr last, the last vac should be as low as possible so aim for 2 torr.
    I would advise regular checks of the vac pump oil and replacement at regular intervals as well.

    Cheesr taz.
    Last edited by taz24; 06-04-2008 at 06:27 PM.

  6. #6
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: Evacuation Procedures

    Thanks alot !

Similar Threads

  1. Triple evacuation
    By kpapa in forum Fundamentals
    Replies: 32
    Last Post: 22-02-2010, 10:35 PM
  2. Evacuation
    By tadipatrir in forum Fundamentals
    Replies: 10
    Last Post: 14-09-2007, 11:56 PM
  3. Evacuation, How deep should it be?
    By kengineering in forum Technical Discussions
    Replies: 13
    Last Post: 04-01-2006, 10:26 PM
  4. Burn out procedures
    By reggie in forum Fundamentals
    Replies: 13
    Last Post: 22-01-2003, 06:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •