    hitachi chiller



    hi i was having a problem with high amps on the chillers compressor ,also i had 11.c going into condensor (water cooled ) and 36 coming out.
    i thought it was just the regulating valve for the flow causing the problem.
    but with the high tds across the condensor coil would this be the cause



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hitachi chiller

    36 coming out seems OK!
    You need more measurements!
    Superheat, subcool, TD at evaporator , pressures etc...

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: hitachi chiller

    Any chance we could get a bit more information?

    Model No.?
    Pressures?
    Subcooling?
    Superheat?
    Chilled water in/out?

    Would be a good start......


    We are good but not that good and definitely not psychic...
    Last edited by The Viking; 04-04-2008 at 09:25 PM.

  4. #4
    Join Date
    Apr 2008
    Location
    england
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: hitachi chiller

    hi yeah didint get chance to get all facts as
    chiller would trip out on overload 90 amps before i
    could get a chance to get everything
    5 bar suction 16 bar discharge
    11.c in , 36.c out ( condensor)
    set point was 9.c with 19 return evap

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hitachi chiller

    Quote Originally Posted by ncmorgan View Post
    hi yeah didint get chance to get all facts as
    chiller would trip out on overload 90 amps before i
    could get a chance to get everything
    5 bar suction 16 bar discharge
    11.c in , 36.c out ( condensor)
    set point was 9.c with 19 return evap
    Did you checked crankcase heater? Did you energized heater at least 12-24 hours before start of compressor? Did you checked presence of all 3 phases and voltage balance at compressor terminal ( no more then 5% difference)?
    Last edited by nike123; 04-04-2008 at 09:47 PM.

  6. #6
    Join Date
    Apr 2008
    Location
    england
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: hitachi chiller

    Quote Originally Posted by nike123 View Post
    Did you checked crankcase heater? Did you energized heater at least 12-24 hours before start of compressor? Did you checked presence of all 3 phases and voltage balance at compressor terminal ( no more then 5% difference)?
    yeah all 3 phases fine, plant is about 8 years old
    and crankcase heaters on,plant flow for condensor
    water is all ok,no history of blocked condensor.
    i do think for a water cooled condensor 25.c across
    the coil is a bit high,thats why i thought the flow reg was not operating fully and causing not enough flow though condensor,causing high hp and amps

  7. #7
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: hitachi chiller

    Did it sound normal?
    Is the windings' resistances normal?
    Does it megger out OK?
    Is the voltage OK on all 3 phases at the compressor's terminals?

    If it drops out on overload before you get a chance to check how it's running, then you are most likely looking for a problem with the compressor itself or the power supply to it.

    (Lack of flow through the condensor will cause a HP trip, and 16 Bar is not excessive in a "normal" installation)
    Last edited by The Viking; 04-04-2008 at 10:00 PM.

  8. #8
    Join Date
    Apr 2008
    Location
    england
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: hitachi chiller

    Quote Originally Posted by The Viking View Post
    Did it sound normal?
    Is the windings' resistances normal?
    Does it megger out OK?
    Is the voltage OK on all 3 phases at the compressor's terminals?

    If it drops out on overload before it gets you get a chance to check how it's running, then you are most likely looking for a problem with the compressor itself.
    yeah done all that ,all ok and checked,back on mon with new reg to see if it works let you know.
    thanks for all your help

  9. #9
    Join Date
    Mar 2005
    Location
    Birmingham U.K.
    Age
    70
    Posts
    54
    Rep Power
    20

    Re: hitachi chiller

    Quote Originally Posted by ncmorgan View Post
    hi i was having a problem with high amps on the chillers compressor ,also i had 11.c going into condensor (water cooled ) and 36 coming out.
    i thought it was just the regulating valve for the flow causing the problem.
    but with the high tds across the condensor coil would this be the cause

    Is the compressor fully loaded on running ?


    you need to make sure the compressor is running unloaded for some time and then bring compressor up to its full 100% capacity.

    regards bobjob

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hitachi chiller

    Quote Originally Posted by ncmorgan View Post
    yeah all 3 phases fine, plant is about 8 years old
    and crankcase heaters on,plant flow for condensor
    water is all ok,no history of blocked condensor.
    i do think for a water cooled condensor 25.c across
    the coil is a bit high,thats why i thought the flow reg was not operating fully and causing not enough flow though condensor,causing high hp and amps
    You have 25K across the coil because the water regulating valve works his job. Entering temperature of water is low, and flow is reduced, in order to pressure in condenser stay at 16 bar, as adjusted at valve.
    That confirms water temperature of 36°C at outlet of condenser.
    If, for example, entering water temperature of 25°C is the case, outlet water temperature with correctly functioning valve should stay at 36°C but water flow will be much higher.
    Last edited by nike123; 05-04-2008 at 07:01 PM.

  11. #11
    Join Date
    Jul 2006
    Location
    uk
    Age
    45
    Posts
    49
    Rep Power
    0

    Re: hitachi chiller

    sounds like the compressor requires a bearing overhaul. Check oil level first. I would also disconnect the compressor leads off the contactors and check the voltages there to ensure you have no faulty contactors.

  12. #12
    Join Date
    Jan 2008
    Location
    Manchester, Uk
    Age
    53
    Posts
    57
    Rep Power
    17

    Re: hitachi chiller

    Hiya, Have you tried running the compressor with only 50 or 75% load for 10mins or so. You should be able to get an idea of what is causing the trip, Have you got a decent superheat. Is the refrigerant charge correct. Have you checked the water strainer for blockage.although the 25oC differential across condenser is not too high. Have you got a dodgy contactor or overload. It might be wise to have condition monitoring on the compressor to see if there is wear on the bearings. A bit expensive to have this done but will tell you if a bearing is on its way out. What run hours has the compressor done, and has it been overhauled in its life. I think it's every 12000hrs for a Hitachi screw, but don't quote me on that. We have a site with 9 of these and have the compressors monitored every six months, we have just started getting significant bearing wear on one of them. Regards, Andy C.

  13. #13
    Join Date
    Apr 2008
    Location
    england
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: hitachi chiller

    hi all just to let you know,my problem was a simple one.it was just a faulty condensor water regulator that wasnt opening correctly,changed regulator and found everything ran sweet.
    thanks for all your replys ,happy fixing

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: hitachi chiller

    Quote Originally Posted by ncmorgan View Post
    hi all just to let you know,my problem was a simple one.it was just a faulty condensor water regulator that wasnt opening correctly,changed regulator and found everything ran sweet.
    thanks for all your replys ,happy fixing
    I am confused.

    Does that mean that valve has not regulated condensation at all the operation times and that sometimes tripped high amperage protection, or condensation temperature of refrigerant at 16 bar was to high for that chiller.
    What refrigerant is in that chiller?

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  3. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  4. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  5. Hitachi samurai chiller problem!
    By THERMOACC in forum Trouble Shooting
    Replies: 2
    Last Post: 28-05-2006, 09:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •