    Variable Speed Control



    Hi Every Body,

    I am very glad being a member of RE forum.

    I have a question: I want to change my 3 kw scroll compressor to VARIABLE SPEED one.
    Firstly I will add frequency converter to change main line frequency of the compressor.
    But I don't know how can I control the system, P, PI, PD or PID ??
    And what kind of hardware I need for this control ??

    Thanks so much.. OE



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Variable Speed Control

    Quote Originally Posted by O_E View Post
    Hi Every Body,

    I am very glad being a member of RE forum.

    I have a question: I want to change my 3 kw scroll compressor to VARIABLE SPEED one.
    Firstly I will add frequency converter to change main line frequency of the compressor.
    But I don't know how can I control the system, P, PI, PD or PID ??
    And what kind of hardware I need for this control ??

    Thanks so much.. OE
    Why you whant do that?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Variable Speed Control

    What is the compressor serving ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2008
    Location
    US
    Posts
    9
    Rep Power
    0

    Re: Variable Speed Control

    This scroll compressor is serving for chiller system. And this is a project for PhD study. I need detailed controlling info if this system changes variable speed
    also inverter system info.
    (system; 3 kw scroll compressor, air cooled condenser and condenser in a channel which temp and flow rate can be change, 12/7 celcius water in evap, TXV and on/off control with carel mc2)

    thanks

  5. #5
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Variable Speed Control

    It is several ways to do the control logic. If you dont have a PLC to control the system I sugests you install a pressure sensor in the suction line, connect it to the VFD and set up the internal PI regulator of the VFD to calculate the necessarry Hz to maintain selected set point suction pressure. You will then get a constant suction pressure regardles of variations in water temp and flow. Alternatively you could install temp sensors in the entering and/or leaving water flow, connect to the VFD, and use one or both of them as the input signal to the PI regulator in the VFD. In that case you will be able to maintain a constant leaving water temp. The entering water temp will be more prone to fluctuation.

    Dont use the D function in the regulator, only the PI function.

    You also ned to take care of short cycling protection and define some parameters to stop the compressor at low heat load. All this should be possible to configure in the setup of the VFD without any need for additional hardware.

    The only compressor specific hardware you need is a HP/LP safety switch controlling a contactor in the mains circuit and a circuit breaker for the VFD.


    Do a search for VFD on the forum. You should be able to find some information here.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Variable Speed Control

    Do you want to change compressor with one real inverter compressor, or you just want control speed of fixed speed compressor with VFD?

    If that is the case, you need to change TEV to EEV because TEV cannot control evaporator in all capacity range of inverter compresor.


    Carel MC2 cannot do control of compressor speed continuously! It can control speed of condenser fan but control of compressor speed could be in only 4 steps (speeds).

  7. #7
    Join Date
    Jul 2005
    Location
    Detroit,USA
    Age
    52
    Posts
    31
    Rep Power
    0

    Re: Variable Speed Control

    Quote Originally Posted by O_E View Post
    Hi Every Body,

    I am very glad being a member of RE forum.

    I have a question: I want to change my 3 kw scroll compressor to VARIABLE SPEED one.
    Firstly I will add frequency converter to change main line frequency of the compressor.
    But I don't know how can I control the system, P, PI, PD or PID ??
    And what kind of hardware I need for this control ??

    Thanks so much.. OE
    I've thought of doing the same thing for my home AC/HP system. The problem is that the compliant scroll design uses the centrifugal force to keep the scroll walls together. I've read some examples of guys who have done it and they were recommended to stay above 40hz by Copeland to keep blowby gasses to acceptable levels. (Don't take that statement as fact, as I really am not sure of the source)

    I'm sure you could run a scroll at a lower speed, but will the oil still be picked up? Will the compressor isentropic efficiency suffer more than the efficiency gains in heat exchangers and blowers/pumps?

    So for me, 60Hz to 40Hz it's not much of a variable speed system, and I'm thinking not worth the trouble.

  8. #8
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Variable Speed Control

    Scrolls isn't the optimum commpressor to speed regulate due to a high minimum Hz. However it is possible to run Copeland scrolls up to 70 or 75 Hz. The voltage must be high enough tho. Select a 230V compressor if the mains is 400V. The VFD then can regulate the correct voltage, ie suply a 230V 50Hz motor with the correct 322 volt at 70Hz.

  9. #9
    Join Date
    Apr 2008
    Location
    US
    Posts
    9
    Rep Power
    0

    Re: Variable Speed Control

    Quote Originally Posted by Erik Detroit View Post
    I've thought of doing the same thing for my home AC/HP system. The problem is that the compliant scroll design uses the centrifugal force to keep the scroll walls together. I've read some examples of guys who have done it and they were recommended to stay above 40hz by Copeland to keep blowby gasses to acceptable levels. (Don't take that statement as fact, as I really am not sure of the source) I'm sure you could run a scroll at a lower speed, but will the oil still be picked up? Will the compressor isentropic efficiency suffer more than the efficiency gains in heat exchangers and blowers/pumps? So for me, 60Hz to 40Hz it's not much of a variable speed system, and I'm thinking not worth the trouble.
    I have read some research paper, according these, scroll compressors are able to operate between 25-60 Hz unless any problem (include lubrication, vibration etc.) with 30% performance improve.
    By the way, do you think still apply VFD to your scroll comp. And what kind of control do you think?

    Quote Originally Posted by SteinarN View Post
    It is several ways to do the control logic. If you dont have a PLC to control the system I sugests you install a pressure sensor in the suction line, connect it to the VFD and set up the internal PI regulator of the VFD to calculate the necessarry Hz to maintain selected set point suction pressure. You will then get a constant suction pressure regardles of variations in water temp and flow. Alternatively you could install temp sensors in the entering and/or leaving water flow, connect to the VFD, and use one or both of them as the input signal to the PI regulator in the VFD. In that case you will be able to maintain a constant leaving water temp. The entering water temp will be more prone to fluctuation. Dont use the D function in the regulator, only the PI function. You also ned to take care of short cycling protection and define some parameters to stop the compressor at low heat load. All this should be possible to configure in the setup of the VFD without any need for additional hardware. The only compressor specific hardware you need is a HP/LP safety switch controlling a contactor in the mains circuit and a circuit breaker for the VFD.Do a search for VFD on the forum. You should be able to find some information here.
    Thanks for very useful reply, but I couldn't find useful VFD driver info in my searches. Generaly VFD information says you can use PID control. You said use only P and I function (not D function), I couldn't understant exactly.
    I wonder if I need any calculation (except set output water temp.) for the system after connect sensor to VFD input regulator. I don't have enough electronic and control background.
    Please, could you explain detailed information about control of compressor, VFD, sensors, EEV ( a scientific research was used TXV with variable scroll comp effieciently) in this kind applications.
    (this compressor is ZR28K3 PFJ 522 with R134a in 50 Hz 220 V)

  10. #10
    Join Date
    Apr 2008
    Location
    US
    Posts
    9
    Rep Power
    0

    Re: Variable Speed Control

    Quote Originally Posted by nike123 View Post
    Do you want to change compressor with one real inverter compressor, or you just want control speed of fixed speed compressor with VFD? If that is the case, you need to change TEV to EEV because TEV cannot control evaporator in all capacity range of inverter compresor.Carel MC2 cannot do control of compressor speed continuously! It can control speed of condenser fan but control of compressor speed could be in only 4 steps (speeds).
    I don't want to change compressor. I will use VFD and I don't know how can I control it. You said compressor speed can be control in only 4 speeds (steps) by carel mc2, so should I change this for PI,PD,PID (I don't know which one I will use) control or not ?
    And some researcher had used TXV with variable speed scroll more efficient than EEV with fuzzy control. Also I want to compare fuzzy control with conventional one (PI,PD,PID).If you have much more infor please give me.

  11. #11
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Variable Speed Control

    Quote Originally Posted by O_E View Post
    (this compressor is ZR28K3 PFJ 522 with R134a in 50 Hz 220 V)
    The PFJ motor code tells it's a 1-phase motor. Not possible to speed regulate with a VFD or any other method.

    To not use the D-function you set zero or off to the D-function value in the VFD.

    I suggests you download the full installation/configuration manual for a VFD and study it thoroughly. You also need some electrical knowlegde to be able to set up such a system.

    If you use the internal PI regulator of the VFD you dont need any other calculations. Set the suction pressure if you use a suction pressure sensor. Or set the temperature if you use a temperature sensor.

    If my momory serves me right Copeland scrolls can operate between 35 and 60 or 70Hz.

    It shoud not be any problem with using a TEV on a system like this operating in a capasity range of roughly 50-100%.
    Last edited by SteinarN; 09-04-2008 at 08:42 AM.

  12. #12
    Join Date
    Dec 2007
    Location
    Alaska USA
    Age
    71
    Posts
    10
    Rep Power
    0

    Re: Variable Speed Control

    Hi, I'm still new to this forum.
    If, O-E want control water temperature. On single phase compressor, you can't use VFD. I think you have a other way to control. You can use hot gas bypass ( inject hot gas to inlet of the chiller coil).
    What you guys think?

    tedre

  13. #13
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Variable Speed Control

    Tedre It is a school project so lets let him learn!

    Ensure to use a balanced port TXV as it will take in stride the regulation of the compressor.

    Your control system is to act as a analog feed back loop, so as one set point changes as does the other to balanced it, that is the true goal of this is to have it balance, With that said what is the best point to measure? I would think the water temp as it is our final goal.

    What of the condenser though? As the compressor slows we are allowed to flood more of it to yield better sub cooling at no cost of head pressure due to reduced capacity! I think wise to place a VFD here feeding off head pressure

Similar Threads

  1. Replies: 15
    Last Post: 17-04-2009, 03:50 PM
  2. Variable Speed Butane Comp.
    By Inalex in forum Domestic
    Replies: 5
    Last Post: 09-02-2008, 05:57 PM
  3. Speed control of the compressor
    By Peter_1 in forum Air Conditioning
    Replies: 10
    Last Post: 19-12-2007, 07:51 AM
  4. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  5. Variable speed screw compressors