    Frick RWB II 177H 400 Hp problems



    I have a 400 horse screw in my ammonia refrigerated plant that is giving me fits. We manufacture ice as well as store in two vaults.

    The screw runs fine until it has been at 100% with a slide stop of 3.6 to 3.8 VI for five minutes or so then sounds as if somebody is hitting the brakes on it. The amps jump to high shutdown and off it goes.

    I have calibrated it, changed the oil, replaced the slide stop and slide valve Yuken valves, and had the motor checked by my local motor rebuild shop. The motor seems to be in good shape and thermal scan shows no significant problems in the starter can.

    Anybody ever have one do this???



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Frick RWB II 177H 400 Hp problems

    Quote Originally Posted by warrenbuddy View Post
    I have a 400 horse screw in my ammonia refrigerated plant that is giving me fits. We manufacture ice as well as store in two vaults.

    The screw runs fine until it has been at 100% with a slide stop of 3.6 to 3.8 VI for five minutes or so then sounds as if somebody is hitting the brakes on it. The amps jump to high shutdown and off it goes.

    I have calibrated it, changed the oil, replaced the slide stop and slide valve Yuken valves, and had the motor checked by my local motor rebuild shop. The motor seems to be in good shape and thermal scan shows no significant problems in the starter can.

    Anybody ever have one do this???
    Seems you have liquid in suction ..... compressor screaming.... oil pressure became crazy.... amperes high because you pump liquid with compressor for that reason compressor must be almost completely cold even little iced from outside or at least cold wet.....discharge pipe also cold....

    switch it on and stay around and check all said, with your hand on emergency stop switch....

    .... I know it is terrible noise ....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Similar Threads

  1. Carrier 30XA Liquid chiller Problems
    By Ed Burris in forum Commercial
    Replies: 7
    Last Post: 13-08-2010, 08:12 PM
  2. samsung rs21dcns problems
    By slovenian ian in forum Trouble Shooting
    Replies: 2
    Last Post: 03-11-2007, 03:19 AM
  3. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Replies: 11
    Last Post: 16-02-2006, 04:52 PM
  4. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •