    Thumping noise in the compressor



    I had a call today regarding a thumping noise coming from a compressor. The guy never checked the compressor resistance. He suspected the Outdoor board and replaced it. The system ran for two weeks and failed again. He says he weighed refrigerant charge per the data plate with short run on piping. The system was installed two months ago. Elevation has not been exceeded. This got me to thinking about the megger suggestions you guys gave me. Could it be possible to have small short to ground and system run for for two weeks and take out the outdoor board again. I did recommend the voltage balance check as well as the diode check for the IPM. Im thinking a megger is needed in this situation. What you guys think?



  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Thumping noise in the compressor

    Husky,

    I'm gonna simplify what I think your saying.

    The thumping noise is the compressor short cycling or trying to start. The outdoor board is maybe an electronics control board. Is this an A/C or HP unit?

    When you say failed again, are we talking about the board?

    A compressor that short cycles or is hard starting will play havoc on the electrical controls, wiring, etc.

    Check it while your there. Add a hard start kit if starting is the issue. If you see short cycling then your going to need to put the guages on it and find the cause.

    Regards.............Powell

  3. #3
    Join Date
    Feb 2008
    Location
    India
    Age
    43
    Posts
    28
    Rep Power
    0

    Re: Thumping noise in the compressor

    Was this compressor failure to start & giving jamming noise.Was oil present in te system.check compressor resistance(for grounding or earthing problem) & oil for acid test.

  4. #4
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: Thumping noise in the compressor

    Sorry for the lack of info: The compressor was trying to start. Its a DC Inverter system ( Sanyo ) On the call for cooling the outdoor fan would run but a thumping noise was coming from the compressor. He said resistance was equal across the windings. This happend before and he replaced the outdoor board. The system ran for two weeks and same thing happend again. System would try to start and thumping noise from the compressor. He described it as someone tapping the top of the compressor. He said he would test the compressor with a megger and get back to me

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Thumping noise in the compressor

    Sound mechanical to me, did you try to listen with a stethoscope?

  6. #6
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Thumping noise in the compressor

    Quote Originally Posted by Husky250 View Post
    The system ran for two weeks and same thing happend again. System would try to start and thumping noise from the compressor.
    If the compressor ran for two weeks after the first repair then it should be ok.

    Can you let us know what we are we dicussing here? HP, model of compressor, voltage at the job etc.

  7. #7
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: Thumping noise in the compressor

    H/P Sanyo Inverter system 12,000 BTU
    Voltage = 118 v
    Installed= 3/20/07
    Not sure of compressor model number

  8. #8
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Thumping noise in the compressor

    I'd check with Sanyo and get their recommended hard start kit. A solid state device would probably work ok, but check with them.

  9. #9
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: Thumping noise in the compressor

    Thanks alot !

Similar Threads

  1. Testing Inverters
    By fridge doctor in forum Air Conditioning
    Replies: 38
    Last Post: 15-06-2011, 06:52 AM
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  3. Window AC - "Squeak" Noise when compressor turns off
    By John721 in forum Air Conditioning
    Replies: 3
    Last Post: 30-08-2007, 05:56 PM
  4. noise inverter compressor
    By Airclima in forum Air Conditioning
    Replies: 1
    Last Post: 26-07-2007, 11:42 PM
  5. Abnormal noise from compressor
    By mano in forum Trouble Shooting
    Replies: 1
    Last Post: 09-02-2007, 11:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •