Re: Condensate Lines
Hi Matt,
its not a good idea having excessive condensate pipework in a low temp store. Even worse is having all connected up together as you describe.
My golden rules are......
1. Short condensate pipe as possible.
2. Individual heater tape per cooler.
3. Self limiting external heater tape, with insulation (lagging to us brits & nordic invaders)
4. Compression joints on pipe fittings. This allows easy removal for cleaning/repair work.
5. Indicator lamp on control panel proving power supply to heater tape + indicator lamp for defrost circuit breaker or fuse.
6. Regular inspection (maintenance)
OH, plus keep a wooly hat & a good coat in the van for thoose long hours which you may have to spend chipping ice away.
Billy Ray
-
01-04-2008, 08:21 PM #3
Re: Condensate Lines
Originally Posted by Billy RayIf all else fails, ask for help.
-
02-04-2008, 08:12 PM #4
Re: Condensate Lines
Dear Viking,
hope comment was taken in the manner that it was sent.
Biily Ray
p.s. do you sail you long boat up the Thames!!
Similar Threads
-
Rising lines
By zapoy in forum FundamentalsReplies: 8Last Post: 05-05-2008, 07:53 AM -
Hartell Condensate Pump
By Grizzly in forum Air ConditioningReplies: 8Last Post: 03-01-2008, 09:08 AM -
condensate lines
By kDawg in forum DomesticReplies: 6Last Post: 20-12-2006, 10:28 PM -
LG condensate
By gwilliamson in forum Air ConditioningReplies: 11Last Post: 10-05-2006, 09:48 PM -
Cooling condenser of split with condensate from evaporator
By smileypete in forum Air ConditioningReplies: 11Last Post: 10-07-2005, 08:21 AM