    Condensate Lines



    I have a large freezer with 3 evaporator coils. 1 coil maintains a temperature of -22 deg. F/ 2 coil -20 deg F/ 3 coil -20 deg F. They have a common drain line that runs from coil 3 until it exits out of the freezer 120' later. When we have an issue with defrost with one coil it freezes the line and we spend about 2 days with a torch to melt ice to clear the line and or drain pan. One idea I had was to exit each coil indivivualaly out of the freezer but the condensate water would dump into a grass area that has very little drainage for it to run into the ditches. Another idea was to run each line out the freezer into the floor drain like it is now but no into a common line. Please send any ideas this is a very expensive problem that needs addressed. All lines are insulated and have heat trace.
    Thank you in advance.
    Last edited by MattR11; 01-04-2008 at 02:37 PM. Reason: More information needed.



  2. #2
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Condensate Lines

    Are the lines insulated? Do they have heat trace? If the don't I would suggest wrapping heat trace around the pipe and insulate.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Condensate Lines

    Have you got trace heater and lagging fitted to the drain?

    Edit:
    Ooops,
    I need touch typing lessons.

    At least great minds think alike...

  4. #4
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Condensate Lines

    Whats lagging Viking?

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Condensate Lines

    Aha,
    I do like it when we find the language differences that exist across the pond....

    It's what you would call insulation.

  6. #6
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Condensate Lines

    Thanks, nice web site you have.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Condensate Lines

    Quote Originally Posted by nh3wizard View Post
    Are the lines insulated? Do they have heat trace? If the don't I would suggest wrapping heat trace around the pipe and insulate.
    Quote Originally Posted by The Viking
    Have you got trace heater and lagging fitted to the drain?
    Quote Originally Posted by MattR11
    All lines are insulated and have heat trace.

    Guys, it is time to tee and bear! (and maybe for little Apsint, depending on preferences)
    Last edited by nike123; 01-04-2008 at 03:15 PM.

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Condensate Lines

    Quote Originally Posted by nike123 View Post
    Guys, it is time to tee and bear! (and maybe for little Apsint, depending on preferences)
    Nike,

    The line "

    All lines are insulated and have heat trace."
    Has been added after the first replies.....

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Condensate Lines

    Matt,

    How long are the pipes between the driptrays and the Ts in the drain pipe?

    P.S. When you answer follow up questions, it's easier to find and considered more polite to use the "reply" function instead of the "edit" one....

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Condensate Lines

    Quote Originally Posted by The Viking View Post
    Nike,

    The line "

    All lines are insulated and have heat trace."
    Has been added after the first replies.....
    That still doesn't mean that is not the time for tee and etc...

  11. #11
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Condensate Lines

    Hi Matt,

    its not a good idea having excessive condensate pipework in a low temp store. Even worse is having all connected up together as you describe.

    My golden rules are......

    1. Short condensate pipe as possible.

    2. Individual heater tape per cooler.

    3. Self limiting external heater tape, with insulation (lagging to us brits & nordic invaders)

    4. Compression joints on pipe fittings. This allows easy removal for cleaning/repair work.

    5. Indicator lamp on control panel proving power supply to heater tape + indicator lamp for defrost circuit breaker or fuse.

    6. Regular inspection (maintenance)

    OH, plus keep a wooly hat & a good coat in the van for thoose long hours which you may have to spend chipping ice away.

    Billy Ray

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Condensate Lines

    Quote Originally Posted by Billy Ray
    ...with insulation (lagging to us brits & nordic invaders)
    Ouch. That should generate some comments!
    If all else fails, ask for help.


  13. #13
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Condensate Lines

    Dear Viking,

    hope comment was taken in the manner that it was sent.

    Biily Ray

    p.s. do you sail you long boat up the Thames!!

Similar Threads

  1. Rising lines
    By zapoy in forum Fundamentals
    Replies: 8
    Last Post: 05-05-2008, 07:53 AM
  2. Hartell Condensate Pump
    By Grizzly in forum Air Conditioning
    Replies: 8
    Last Post: 03-01-2008, 09:08 AM
  3. condensate lines
    By kDawg in forum Domestic
    Replies: 6
    Last Post: 20-12-2006, 10:28 PM
  4. LG condensate
    By gwilliamson in forum Air Conditioning
    Replies: 11
    Last Post: 10-05-2006, 09:48 PM
  5. Cooling condenser of split with condensate from evaporator
    By smileypete in forum Air Conditioning
    Replies: 11
    Last Post: 10-07-2005, 08:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •