    Exploding Daikin Outdoor Unit



    Wow,

    I just came back from a callout in London.

    Original call was that the A/C in the Tech office didn't work (this is in the building that watches most of the CCTV cameras in northern London).

    Arrived at site and the indoor unit was completely dead, when I went up to the roof to have a look I almost fell off it!

    I just couldn't believe my eyes

    Where the outdoor unit should have been, there were only wrangled bits of metal! It looked like a 40 tonne truck had gone straight over it at 70mph
    I eventually found part of the compressor embedded in the chiller's condensor.

    This is on a RZQ/FHQ100B system we installed after Christmas.

    The proverbial will really hit the fan tomorrow, as this is on a council building I don't even want to think about all the H&S red tape we will have to deal with.

    Have anybody had this happened to them in the past, or got any ideas as to what could have happened???

    I can't see a reason for the pressure to build up enough to blow the compressor apart, surely the copper tubes must be weaker??

    The pictures I took is to large to be attached here but click HERE for some really scary pictures of it.

    I guess it was lucky that nobody were on the roof when it blew!



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Exploding Daikin Outdoor Unit

    Nice pictures of the unit.

    And yes... I have heard of this happening. Peter_1 (another moderator) and I helped someone down in South Africa with something just like what you described.
    If all else fails, ask for help.


  3. #3
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Exploding Daikin Outdoor Unit

    Viking, you little tinker
    Always easy on the eye.

  4. #4
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: Exploding Daikin Outdoor Unit

    Maybe you had a visit from this guy

    http://youtube.com/watch?v=8gFTnJuYs6M

    If it ain't broke, it doesn't have enough features yet.


    Damo

  5. #5
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Exploding Daikin Outdoor Unit

    Viking
    What are the high pressure safety device on this model ?

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Exploding Daikin Outdoor Unit

    Anyone see the flying Penguins on BBC Breakfast yesterday???

  7. #7
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Exploding Daikin Outdoor Unit

    that is scary coulda taken your head clean off

  8. #8
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: Exploding Daikin Outdoor Unit

    Or Franks flying penguins could have misjudged the landing

    http://www.youtube.com/watch?v=nrxmp...&feature=bz301
    If it ain't broke, it doesn't have enough features yet.


    Damo

  9. #9
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Exploding Daikin Outdoor Unit

    Nice one

  10. #10
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Exploding Daikin Outdoor Unit

    Frank,
    I actually believed that one.F--k I really did.

  11. #11
    Join Date
    Feb 2008
    Location
    India
    Age
    43
    Posts
    28
    Rep Power
    0

    Re: Exploding Daikin Outdoor Unit

    result of faulty pressure safety valves or no safety vale installed or wrong selection of safety vale installed

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Exploding Daikin Outdoor Unit

    Quote Originally Posted by praveen View Post
    result of faulty pressure safety valves or no safety vale installed or wrong selection of safety vale installed
    Yes, sure it is!!!

    Did you checked picture of actual scene?
    http://www.the-viking.eu/photos/id77.html
    Last edited by nike123; 02-04-2008 at 08:36 AM.

  13. #13
    Join Date
    Sep 2007
    Location
    Philippines
    Posts
    12
    Rep Power
    0

    Re: Exploding Daikin Outdoor Unit

    most probably blocked system.

  14. #14
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Exploding Daikin Outdoor Unit

    Please look at the date of my original post...

    If you clicked on the link, you had ended up on a page stating [you been April fooled]...

    Let's us let this thread die now until next year when I will come up with something new.

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Exploding Daikin Outdoor Unit

    Might be an idea to 'Close' it Viking and perhaps remove your 'link' otherwise you'll be stuck with having to keep that web page active for ever
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Exploding Daikin Outdoor Unit

    I don't think a few of our non-UK members understand April fools day...lol

    Everyone that posted a normal answer is from abroad and the other one is from Essex.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  17. #17
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Exploding Daikin Outdoor Unit

    Quote Originally Posted by chillin out View Post
    I don't think a few of our non-UK members understand April fools day...lol

    Everyone that posted a normal answer is from abroad and the other one is from Essex.

    Chillin
    Silly me, as a foreigner myself, I have found April fools day quite universal..but I do see your point about Essex

    I did try and find a way of locking the thread but I suspect that you have to be a mod to do that, perhaps one of you guys could help me?

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Exploding Daikin Outdoor Unit

    Quote Originally Posted by The Viking View Post
    Silly me, as a foreigner myself, I have found April fools day quite universal..but I do see your point about Essex

    I did try and find a way of locking the thread but I suspect that you have to be a mod to do that, perhaps one of you guys could help me?
    I think that every thread that you started, you could lock!

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  4. Daikin VRVIII Install - Sub Contract
    By gwilliamson in forum Air Conditioning
    Replies: 7
    Last Post: 07-02-2008, 09:00 PM
  5. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •