    Water Chiller Control



    We were asked to look at a chiller with control problems.

    It is a stand alone unit which serves two ahu. The unit operates when a set of external volt free contacts complete a circuit.

    Chilling to the ahu is controlled by the BMS and mechanical valves.

    The external contacts are controlled via a small pressurization unit, which consists of a header tank, pump and high & low pressure switches.

    The pressurization unit pumps is connected via water piping to the chilled water ring.

    Can anyone shed any light as to how the control logic is meant to work.

    Thanks

    David



  2. #2
    Join Date
    Apr 2003
    Location
    UK
    Posts
    20
    Rep Power
    0
    The pressurization unit mainly, leading on to the chiller.

  3. #3
    Join Date
    Jul 2006
    Location
    uk
    Age
    45
    Posts
    49
    Rep Power
    0

    Re: Water Chiller Control

    What sort of control problems are you getting? I can't see the pressurization unit sending the enable signal though although it might be an interlock. I would suggest attending site with the controls company to determine which is at fault, the chiller or the controls.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Water Chiller Control

    Quote Originally Posted by David PS View Post
    ...The external contacts are controlled via a small pressurization unit, which consists of a header tank, pump and high & low pressure switches.
    The pressurization unit pumps is connected via water piping to the chilled water ring.
    This needs a small schematic because I don't understand your set-up.
    I think others think the same and if the question is already difficult to understand, then the possible answer will also be wrong or direct you in the wrong direction.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Water Chiller Control

    Have to say folks that we have missed this post somewhat.

    As it is over three years old I would imagine that he has resolved the matter by now
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Chiller Control
    By tabtech in forum Air Conditioning
    Replies: 0
    Last Post: 09-07-2006, 11:40 PM
  2. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM
  3. water chiller
    By andrewuk in forum Technical Speculations
    Replies: 9
    Last Post: 17-10-2005, 09:28 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. water chiller
    By dwallan in forum Air Conditioning
    Replies: 3
    Last Post: 12-12-2001, 03:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •