    Apr 2006
    41
    1,620
    23
    Re: R134a / Water Heat Exchanger Sizing
    A 6,000 BTU coaxial condenser is the most commonly used with good success.
    ACEprod's Avatar
    ACEprod Guest
    MG Pony thanks for your reply,
    I'm building the HE myself so I need the required surface area of copper pipes in order to deliver to the water 500 Watts of cooling load.
    Thanks.
    Apr 2006
    41
    1,620
    23
    If it is just for fun, research some of my old threads, other wise cheaper to simply buy a Hx.
    http://www.refrigeration-engineer.co...ead.php?t=8150
    Here you go.
    ACEprod's Avatar
    ACEprod Guest
    I followed your advice and read some of your older posts and I discovered Dan Cap. I need to clear some things in my mind about refrigeration terms since I new at cooling things! My job is to warm things up not cool them so I need some help.
    When a manufacturer refers to evaporating temperature does it refer to the refrigerant temp. during evaporation or the cooling fluid temp.?
    Thanks once again.
    Apr 2006
    41
    1,620
    23
    the refrigerant temp boiling inside the exchanger, it will need to be 6 or so degrees cooler then your desired fluid temp.
    ACEprod's Avatar
    ACEprod Guest
    Thanks once again MG Pony
    How can we calculate / predict the temperature of R134a at the different stages having an evaporating temp. of 10 C?
  1. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  2. frostles heat pump
  3. heat exchanger for small chiller
    By star882 in forum Fundamentals
    Last Post: 30-01-2007, 12:06 PM
  4. Building a wine cabinet
  5. R134a <-> liquid heat exchanger design
    Last Post: 10-05-2002, 08:36 AM