Results 1 to 19 of 19
  1. #1
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Question Compressors - screw or reciprocating?



    Hi,

    many times on RE forums we had discussion about.... here are, from the first hand some thoughts about....how to save some energy


    Quote Originally Posted by http://www.sabroe.com/information/screw-or-reciprocating.html


    There is no simple answer to the constantly rec
    urring question of whether it is best to use screw compressors or reciprocating compressors. Both types are viable alternatives in virtually all applications, and both types are normally capable of doing the job.



    • capacity required

    Larger screw compressors use less energy, whereas reciprocating compressors are most energy-efficient at capacities less than approx. 1200 kW.


    • operating conditions

    Screw compressors and reciprocating compressors differ greatly in efficiency when not operating at or near their design conditions.
    Screw compressors are significantly less energy-efficient under off-design conditions, especially if they have a fixed internal volume ratio. Screw compressors with variable volume ratio are therefore more efficient.


    • part-load requirements

    If a compressor is to run at part load much of the time, reciprocating compressors are significantly more efficient.


    • energy consumption

    In smaller plants operating at evaporating temperatures of
    -10°C or higher, single stage reciprocating compressors will have lower power consumption than screw compressors. In larger plants, the opposite is the case.
    In applications that operate at lower temperatures, a two-stage installation is the best choice. Power consumption for such a two-stage unit is about the same for both compressor types, depending on plant size.


    • temperature levels

    In air conditioning and other “high-temperature” applications, reciprocating compressors normally use 5–15% less energy than small screw compressors.
    Screw compressors working at lower temperatures, and in larger-size installations, use less energy than the corresponding reciprocating compressors.


    • refrigerant to be used

    The refrigerant usually only directly influences decisions about compressor type when high-pressure refrigerants such as R410A and R744 (CO2) are to be used.
    In such cases, reciprocating compressors have significantly lower energy consumption.


    • ease of maintenance

    Reciprocating compressors have many moving parts compared to screw compressors, which means that more maintenance is needed. However, this maintenance work is relatively simple and can always be done on site.
    With screw compressors, on the other hand, replacements and main overhauls usually mean that the entire compressor has to be sent back to the factory.


    • financial resources

    In smaller plants where one or two reciprocating compressors can handle the requirements, these are normally the cheapest solution.
    The opposite is normally the case in larger plants. One or two screw compressors are normally cheaper than six to eight reciprocating compressors.


    • available space

    Screw compressors are much more compact than reciprocating compressors, especially at larger capacities.
    One single screw compressor with double the capacity can normally replace at least two ”recips”.
    This is "copy&paste" text, but I believe worth to read, more about you can read here:

    http://www.sabroe.com/information/sc...procating.html


    Best regards, Josip



    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  2. #2
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: Compressors - screw or reciprocating?

    Very good read Josip.

    I`ve always liked screws compared to recips but i dont get involved with them as much as i`d like.
    If it ain't broke, it doesn't have enough features yet.


    Damo

  3. #3
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Compressors - screw or reciprocating?

    I do not have any problems with screws, recips or centrifugals as long as they are applied in the proper application.

    A lot of people with limited experience will migrate to a compressor which they have some experience.

    Take for instance the argument that a recip ins terrible and a screw is better....blanket statement.

    I have applied a lot of recips successfully in projects and maintenance hsa not been a problem. The trick is to design the system properly and do not apply the compressors at the extremes of their operating envelopes. Watch the pressure ratios, such superheat and rotational speed.

    One very capable compressor in ***** applications is the carrier 5H and 5F series. They are very reliable machines when selected and rated at 1200 RPM instead of the air conditioning rating of 1800 RPM. The 5H**6 series (long stroke) work as well if you keep the piston speed down to something much less than the 1000 plus feet/ minute range.

    The big thing is to design the system for the proper fit, application and equipment.

    ken

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Compressors - screw or reciprocating?

    Quote Originally Posted by TXiceman
    A lot of people with limited experience will migrate to a compressor which they have some experience.
    Or, it sometimes depends on what the salesman has for sale also. I've seen this go both ways for either recip.'s or screws.

    It's not the compressor so much as it is the application (or available space).

    Th eCarrier open drive recip.'s are hard to beat for ***** applications. I'm looking at these now for a project. Did you know Carrier used to sell these for ammonia service a long time ago?
    If all else fails, ask for help.


  5. #5
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Compressors - screw or reciprocating?

    Quote Originally Posted by US Iceman View Post
    Did you know Carrier used to sell these for ammonia service a long time ago?
    I still know of a couple that are still running, just a few miles away. They look strange sitting next to a Vilter. Carrier still had parts for them a few years ago. I do not know what the parts situation is at the moment.

  6. #6
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Compressors - screw or reciprocating?

    We have a few Sullair ammonia compressors, they don't have any real capacity control, but they are great running screws.

    Thanks for the info Josip

  7. #7
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Compressors - screw or reciprocating?

    Yepper, I know about the Carrier NH3 recips and have also used them on propane service. I still have some of the old propane data around here.

    Also have done several Vilter 440's on propane. If I remember correctly, they went to Israel.

    Also done several screws on isobutane.

    Ken

    ken

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Compressors - screw or reciprocating?

    I always liked the old Sullair screws. It's a shame they got out of the refrigeration business.

    The only isobutane project I worked on was for very high temperature heat recovery using thermosyphons. After all of the research and engineering it seemed it was too risky by the owner and the project was shelved. Too bad really... I thought it was pretty slick.
    If all else fails, ask for help.


  9. #9
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Compressors - screw or reciprocating?

    Isobutane is tricky to work with due to the way the vapor dome slopes off tot he right. The compression lines do go back intot he dome and you have to have a lot of superheat in the suction to get you clear of the saturated vapor line at discharge conditions. Other wise it is a great refigerant.

    Another problem is having long and uninsulated suciton runs in an industrial application. The vapor pressure is so low that it can condense in the suction line at failry warm ambients.

    Ken

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Compressors - screw or reciprocating?

    Quote Originally Posted by TXiceman
    Another problem is having long and uninsulated suction runs in an industrial application. The vapor pressure is so low that it can condense in the suction line at fairly warm ambients.
    Yep, it's close to the way R-114 acted also.

    What you mentioned above is an interesting fact that most people are not aware of. I've seen this happen in suction lines in ammonia systems when they operate for long periods of low capacity.

    During full load the suction pipes are a little colder due to the slightly lower suciton pressures. Then when the compresors unload the suction pressure rises justa bit and the gas starts to condense.

    Refrigerants are funny things sometimes.
    If all else fails, ask for help.


  11. #11
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Compressors - screw or reciprocating?

    Ken's post of 31.03.08 is perfect I wish there were people with similar thoughts in our country.

  12. #12
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Compressors - screw or reciprocating?

    hi,josif,
    that was a balance statement on both type comp.many thanks for the info.

  13. #13
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Compressors - screw or reciprocating?

    You will get a much more balanced approach from a company that has more than one type of compressor to sell. If all you have to sell is screws....guess what, they are the best compressor for every job ...especially if you want to continue to eat.

    I enjoyed working foe many years with a company that could offer screws, recips and centrifugals for a while. It was actually fun to hear some of the "stories" the competitors came up with why you had to use certain type of compressor.

    It also helps to have experienced and open minded engineers...but that seems to be something the industrial industry is loosing.

    I am currently out of the refrigeration field after 37 years. My choosing due to location and $$$$. I can make a lot more at a large EPC firm.

    Ken

  14. #14
    Join Date
    Feb 2008
    Location
    Saudi Arabia
    Age
    52
    Posts
    69
    Rep Power
    17

    Re: Compressors - screw or reciprocating?

    Thanks for the info

  15. #15
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Compressors - screw or reciprocating?

    Hello Josip ,

    thanks for sharing those information .

  16. #16
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: Compressors - screw or reciprocating?

    I have both screws and recips at my facility. the screws have a lot less maintenance issues than the recips and they also load and unload in more precise increments to maintain a constant suction pressure as opposed to recips that load and unload one bank at a time. I personnaly prefer the lower noise levels of the screw compressors

  17. #17
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Compressors - screw or reciprocating?

    Quote Originally Posted by chilldis View Post
    I have both screws and recips at my facility. the screws have a lot less maintenance issues than the recips and they also load and unload in more precise increments to maintain a constant suction pressure as opposed to recips that load and unload one bank at a time. I personnaly prefer the lower noise levels of the screw compressors
    What kind of facility do you work in? Cold storage, manufacturing...

  18. #18
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: Compressors - screw or reciprocating?

    NH3Wizard, I operate a cold storage facility for a major grocery supply chain in the northern US.

  19. #19
    Vinesy's Avatar
    Vinesy Guest

    Re: Compressors - screw or reciprocating?

    if its energy savings your after - yorks YCIV variable speed compressors are one of the best options available at present

Similar Threads

  1. reciprocating compressors vs screw, for NH3
    By lraja in forum Industrial
    Replies: 15
    Last Post: 04-03-2007, 02:30 AM
  2. refcom screw compressors
    By fitter in forum Industrial Compressors
    Replies: 3
    Last Post: 11-11-2006, 02:01 PM
  3. Variable speed screw compressors
    By Friobernal in forum Industrial Compressors
    Replies: 1
    Last Post: 14-11-2004, 09:28 AM
  4. Screw compressors
    By bernard in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 05-06-2004, 05:06 PM
  5. Overhauls on Reciprocating compressors on packs
    By Mark in forum Supermarket Refrigeration
    Replies: 9
    Last Post: 14-03-2004, 02:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •