    replaced cap tube



    Hello everyone.

    Recently replaced a cap tube that was restricted on 2 door commercial fridge.

    Cap tube size and length was recommended to me by wholesaler that used a selection programme to work out length and bore size.

    compressor: electrolux L57TN 444 watts@-5 32 deg ambient 55 deg cond temp.

    refrigerant: R22

    Recommended length was 1.85metres of 0.9mm which was replaced and drier changed.

    unit is working ok but not quite satisfactory.Gas charge could not be weighed in as it had no name plate.Anyway information as follows.

    Cabinet temp: 4 deg c
    suction: 340 kpa (49psi)
    discharge: 1730 kpa (250psi)
    liquid line temp: 43 deg c
    suction temp: 28.2 deg c

    The thing that bothers me is the extra superheat
    unit has a small heat exchanger which would explain some extra superheat. If i add more gas to lower the superheat the suction evap temp becomes too high.
    Possibly cap tube length is to short?

    After coming home checked some tables that I have and I think tube may have been better at 2.01 metres of 0.9 mm bore.

    Any help would be appreciated.



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: replaced cap tube

    Most commercial fridges have extra long cap tubes to make up for the fact that the evaps are undersized, and most of them have high superheat anyway.
    Cabinets with a capillary don't run like a healthy balanced refrigeration system on a TX valve. Most of them do have 20k superheat, from domestics to skope and williams commercial cabinets
    Most obvious question is what was the length of the old capillary, was it a different bore or did you not make it the same length for some other reason?

    edit: Now that it's down to temp, did you try disconnecting the evap fan and charging until floodback?
    Last edited by paul_h; 29-03-2008 at 10:07 AM.

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: replaced cap tube

    On a cap tube system with a heat exchanger, with the cabinet down to temperature, I would expect the suction line temperature near the compressor inlet to be 50-60F/10-15C... and the suction pressure to be whatever it wants to be.

  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: replaced cap tube

    Thanks for all who replied.

    Removed capillary and changed to tx valve with reciever,system working perfect now.

  5. #5
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: replaced cap tube

    Quote Originally Posted by Temprite View Post
    Thanks for all who replied.

    Removed capillary and changed to tx valve with reciever,system working perfect now.
    attaboy, capillaries suck compared to txv's
    ...and she said "give it to me you big fridgie"

  6. #6
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: replaced cap tube

    just like to say this sounds way too short a capalliry line for this application , should be 3 metres then it would have worked a treat i bet.

  7. #7
    DAIRYAIR's Avatar
    DAIRYAIR Guest

    Re: replaced cap tube

    Hello, does anyone know cap tube size and length for hussman LBN 5. 1/2 HP, R404a. I have the old tube guess I can measure it but don't know bore size. Just thinking maybe a wire type spark plug gauge if I can find one. Dairyair

Similar Threads

  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Replies: 7
    Last Post: 16-11-2010, 11:44 PM
  2. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Replies: 4
    Last Post: 15-11-2007, 06:03 AM
  3. Coils - Inline vs Staggered tube
    By nh3simman in forum Fundamentals
    Replies: 15
    Last Post: 03-04-2007, 08:25 PM
  4. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  5. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 07:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •