    Automatic oil return system



    Hi there fellas
    Just joined the site and i like what i see
    I myself am getting into the industrial scene
    What are some effective ways for automatic oil return on ammonia systems. I am well aware of the manual draining exercise but just wanted to know are there many effective automatic procedures????
    look forward to the replies



  2. #2
    Join Date
    Mar 2006
    Location
    Philippines
    Age
    53
    Posts
    124
    Rep Power
    19

    Re: Automatic oil return system

    Install a oil separator at the discharge then put auto drain under oil separator going back to your suction.

    Guapo

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Automatic oil return system

    Hi, matt watson

    Welcome to RE forums...

    Quote Originally Posted by matt watson View Post
    Hi there fellas
    Just joined the site and i like what i see
    I myself am getting into the industrial scene
    What are some effective ways for automatic oil return on ammonia systems. I am well aware of the manual draining exercise but just wanted to know are there many effective automatic procedures????
    look forward to the replies
    yes there are.... but must be design within plant from beginning... modifications done later usually are not good...return of dirty oil from the last evaporator back to compressor suction can be very expensive sometimes....

    .... good help is to install special self closed valves (with spring) for oil drain...

    if you loose too much oil then you must search for cause ... automatic oil return will not improve/repair your problem/cause

    .... little smell of ammonia will keep you awake and ever ready

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Mar 2008
    Location
    Dallas, Oregon
    Age
    72
    Posts
    51
    Rep Power
    17

    Re: Automatic oil return system

    I have never heard of an automatic oil draining system on an ammonia system. At my company's facilities we have our oil traps set up so that we may use NH3 pressure to drain the traps into an "oil regenerator", a heated vessel where the oil and ammonia may be separated. (I do not know if there is another name for this separator vessel.) The residual oil is then either used as fuel in our boilers, or it is recycled.

    On a personal note, I would recommend against an automatic oil drain system as it is very important to know how much oil is being removed from the system, and the quality of the oil being removed from the system may indicate serious problems such as moisture or even metal particles in the oil. An automatic system would remove your operators from this important information and might deprive you of the knowledge of troubles to come.
    Last edited by Oregon Jim; 29-03-2008 at 04:15 PM.

  5. #5
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Automatic oil return system

    Just to clear up any possible confusion, let us understand what we are discussing.

    We have refered to oil return on the discharge separator. This is essential on many machines.

    Automatic draining of vessels back to a "Oil Still" is not uncommon. It also can be the source of many problems, as the first sign that it has quit working is that the evap fails due to oil logging.

  6. #6
    Join Date
    Mar 2008
    Location
    Dallas, Oregon
    Age
    72
    Posts
    51
    Rep Power
    17

    Re: Automatic oil return system

    Pardon me... I misunderstood.

    "Oil still... I like that better than "regenerator".

    On our discharge separators we have installed sight glasses in the lines so that we have a way of seeing what is being returned. I do not like relying too much on automatic anything. It makes operators less observant.

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Automatic oil return system

    Hi,

    Quote Originally Posted by Oregon Jim View Post
    I have never heard of an automatic oil draining system on an ammonia system. At my company's facilities we have our oil traps set up so that we may use NH3 pressure to drain the traps into an "oil regenerator", a heated vessel where the oil and ammonia may be separated. (I do not know if there is another name for this separator vessel.) The residual oil is then either used as fuel in our boilers, or it is recycled.

    On a personal note, I would recommend against an automatic oil drain system as it is very important to know how much oil is being removed from the system, and the quality of the oil being removed from the system may indicate serious problems such as moisture or even metal particles in the oil. An automatic system would remove your operators from this important information and might deprive you of the knowledge of troubles to come.

    Quote Originally Posted by NH3LVR
    Just to clear up any possible confusion, let us understand what we are discussing.

    We have refered to oil return on the discharge separator. This is essential on many machines.

    Automatic draining of vessels back to a "Oil Still" is not uncommon. It also can be the source of many problems, as the first sign that it has quit working is that the evap fails due to oil logging.
    Yes, I agree it is not a fully automatic oil return system, but closed system with only one drain point...the same as described by Oregon Jim...and supported by NH3LVR ..... language can be a big barrier sometimes

    .... automatic oil return is normal between compressor and discharge separator....

    ... also we can install oil pump with pipe system for charging and draining of oil, kind of semiautomatic operation... because we have to open and close different valves regarding what we are doing...but this is another story

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  4. Oli Return System
    By Andrew Pribora in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 11-10-2004, 04:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •