    having problems with a pu30ek outside unit at the stat it was reading p8 code fixed problem now it is going off on ld7 code in outdoor unit cant find the problem. help?



  2. #2
    Join Date
    Feb 2008
    Location
    stevenage england chav central
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: mitsubishi p series

    hello mate give more info ie model nos outdoor would help sounds like its a older mitsubushi with lights in the outdoor unit ?
    cheers dec

  3. #3
    Join Date
    Feb 2008
    Location
    stevenage england chav central
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: mitsubishi p series

    hello alan ive had a quick look and i think it might be a thermistor fault or a problem with the charge in the sytem affecting the thermistor check the resistance according to the service manual temp resistance value given in a graph or table reading within the tech book

  4. #4
    Join Date
    Feb 2008
    Location
    stevenage england chav central
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: mitsubishi p series

    hello alan found the tech book on the pu30ek online the tech manual says that its a th3 fault the thermisor is connected to the heat exchanger your head pressure could be too high dirty condenser fan coil or maybe you have a shortage of gas hope this helps if you need the tech book send me a message and give me your email address then i will send it too you
    cheers dec
    He who does nothing does nothing wrong !

  5. #5
    Join Date
    Jan 2008
    Location
    qatar
    Age
    51
    Posts
    61
    Rep Power
    17

    Re: mitsubishi p series

    hi this is moorthy from qatar. any body give me details of compressor oil fill systme with picture.

    TRY TO LEARN MORE ABOUT A/C SYSTEM

Similar Threads

  1. New to RE and needing Daikin Help
    By Owen in forum Air Conditioning
    Replies: 20
    Last Post: 25-09-2008, 06:55 PM
  2. Mitsubishi Light Truck Refrigeration
    By Mastercool in forum Transport
    Replies: 2
    Last Post: 23-11-2007, 06:15 AM
  3. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM
  4. 2 chillers in series
    By giovanni in forum Technical Discussions
    Replies: 18
    Last Post: 23-06-2007, 07:08 AM
  5. VRV fault
    By Jase in forum Air Conditioning
    Replies: 10
    Last Post: 16-05-2007, 08:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •