28-03-2008, 12:43 AM #1
mitsubishi p series
having problems with a pu30ek outside unit at the stat it was reading p8 code fixed problem now it is going off on ld7 code in outdoor unit cant find the problem. help?
-
28-03-2008, 09:33 AM #2
Re: mitsubishi p series
hello mate give more info ie model nos outdoor would help sounds like its a older mitsubushi with lights in the outdoor unit ?
cheers dec
-
28-03-2008, 09:52 AM #3
Re: mitsubishi p series
hello alan ive had a quick look and i think it might be a thermistor fault or a problem with the charge in the sytem affecting the thermistor check the resistance according to the service manual temp resistance value given in a graph or table reading within the tech book
-
28-03-2008, 04:38 PM #4
Re: mitsubishi p series
hello alan found the tech book on the pu30ek online the tech manual says that its a th3 fault the thermisor is connected to the heat exchanger your head pressure could be too high dirty condenser fan coil or maybe you have a shortage of gas hope this helps if you need the tech book send me a message and give me your email address then i will send it too you
cheers decHe who does nothing does nothing wrong !
-
29-03-2008, 10:17 AM #5
Re: mitsubishi p series
hi this is moorthy from qatar. any body give me details of compressor oil fill systme with picture.
TRY TO LEARN MORE ABOUT A/C SYSTEM
Similar Threads
-
New to RE and needing Daikin Help
By Owen in forum Air ConditioningReplies: 20Last Post: 25-09-2008, 06:55 PM -
Mitsubishi Light Truck Refrigeration
By Mastercool in forum TransportReplies: 2Last Post: 23-11-2007, 06:15 AM -
Mitsubishi compressor lock
By marc5180 in forum Air ConditioningReplies: 29Last Post: 08-10-2007, 05:48 PM -
2 chillers in series
By giovanni in forum Technical DiscussionsReplies: 18Last Post: 23-06-2007, 07:08 AM -
VRV fault
By Jase in forum Air ConditioningReplies: 10Last Post: 16-05-2007, 08:21 PM