Results 1 to 9 of 9
    May 2002
    The Netherlands
    48
    274
    22
    Capillary tube calculator: surface tension of various refrigerants
    A common question that pops up amongst us overclockers is 'What size captube do I need?', or even worse: 'I have captube XXX; how long does it need to be?'
    To answer those questions, there are tables with information, such as the Cubigel captube sizing table.
    I tried to pour that table with some interpolation into a nice easy-to-use piece of software. I normalised the values in those tables to 1mm I.D. captube, and plotted the data to see what function could be used for interpolation. Then I noticed that there are large jumps in the plot, so it it no good.
    Further research pointed me to a model developed by Wolff et al. (1995). They used the Buckingham pi theorem to predict mass flow. According to them, less than 1% of the experimental results was more than 5% off from the predicted values. Now, that's close enough. And estimating refrigeration capacity from mass flow is no big deal once you know parameters like subcooling and evaporation temperature. Thus, it seems like a good model to pour into a piece of software.
    Wolff's model only uses a parameter which I cannot find in refrigerant datasheets: the surface tension.
    Who can provide this parameter for various refrigerants?
    St. Louis, MO
    509
    Surface tension values for many refrigerants can be obtained from the NIST RefProp program. One can also write code to query the RefProp DLL to obtain these values. Also, as the Prof recalls, the ASHRAE thermophysical properities of refrigerants guide has correlations for surface tension.
    Prof Sporlan
    May 2002
    The Netherlands
    48
    274
    22
    And where could a DIY guy obtain the RefProp program or the correlations mentioned in the ASHRAE manual?
    St. Louis, MO
    509
    Ask, and it will be given you; seek, and you will find; knock, and it will be opened to you. (Matthew 7:7)
    The Prof finds these values for saturated liquid:
    Temp (°F) s (lbf/ft)
    -40 0.001236
    -20 0.001113
    0 0.000992
    20 0.000973
    40 0.000758
    60 0.000646
    80 0.000538
    100 0.000433
    Prof Sporlan
    St. Louis, MO
    509
    Quoted from a book that, when all things added up, means nothing... Prof
    A fine source of adages, regardless of one's beliefs.
    Prof Sporlan
    May 2002
    The Netherlands
    48
    274
    22
    Can I use these values for all the refrigerants? More specific: is the difference in surface tension between various refrigerants low enough to be insignificant?
    St. Louis, MO
    509
    It would be better for your cap tube calculator to use actual values. The Prof has tables for a number of refrigerants.
    Prof Sporlan
    May 2002
    The Netherlands
    48
    274
    22
    Is it possible to send me a set of tables? Personally I think that a cap tube calculation tool would be handy for many people, not just overclockers.
    St. Louis, MO
    509
    For one sizing cap tubes, the complete book will be handy:
    Thermophysical Properties of Refrigerants
    Prof Sporlan
  1. Capillary tube prices in the UK
    By trial in forum Fundamentals
    Last Post: 18-09-2007, 12:16 PM
  2. :rolleyes: capillary tube size in distributor?
    By abbasi in forum New Technologies
    Last Post: 08-07-2006, 03:56 PM
  3. metric capillary tube
    By tralex in forum Fundamentals
    Last Post: 21-02-2006, 06:57 AM
  4. Superheat in Capillary tube systems
    By setrite in forum Technical Speculations
    Last Post: 20-06-2002, 12:08 AM