27-03-2008, 12:46 PM #1
Some unscientific considerations of the utilization of vacuum pumps
The physics behind low pressure gas flow is rather interesting. The resistance of flow in the hoses between the pump and the system does actually increase relatively as the pressure in the system decreases.
We can do a thought experiment:
Lets say we have atmospheric pressure in the system and start to evacuate. In a short time, lets say 10s, the pressure is halved. To halve the pressure once more takes more than 10s. The next halving takes considerably more than 10s. For every halving of the remaining pressure the necessary time increases. It is maybe not easy to understand that without imagine what happens when the system is under an extreme vacuum. Imagine you are a blind gas molecule bouncing accidentally around in the system. At the beginning of the evacuation process you will feel that you have far less molecules at the side of you where it is an outlet to the vacuumpump and you will bounce a longer distance in that direction than you do in the other direction before you bounce into an other molecule. Therefore you will rather quickly bounce yourself toward the outlet of the system. Try to imagine how it will be if the system was under an extreme vacuum and there was only a few gas molecules, lets say 10 molecules, left in the system. You would then be bouncing accidentally around in the system, hitting the walls of the system, but hardly ever hitting an other gas molecule. You would then have very hard to say which way is toward the outlet, and you had to bounce accidentally around for a very long time to recognise that it maybe is slightly fewer molecules in the one direction where the outlet is. Imagine if you was the last gas molecule left in the system. Remember you are blind. How long do you think you have to bounce accidentally around in the system before you find the outlet?. A VERY long time I can assure you!
It is of course not possible, nor necessary to achieve such vacuums we have described here. We don't even reach vacuums as low as tens of billions of molecules left in the system. But to imagine such extreme vacuums is very helpful in order to understand how increased vacuum causes the remaining gas to have harder and harder to find the way out of the system. And that the limiting factor is often not the capacity of the vacuum pump but instead the size and number of the outlets and hoses.
I have a 5 cfm (50Hz) pump. I use that pump on my commercial stationary systems as well as my transport refrigeration systems.
The important thing to be aware of when trying to get a efficient and rapid evacuation is the hoses between the pump and the system. I have made a manifold with four 1/4" shrader connections at the pump. I always use hoses directly from the pump to the system, not through the gauges. It is necessary with at least three 2ft hoses between my 5cfm pump and the system to get a good utilization of this pump. The pump capacity get severely decreased with only two 2ft hoses between the pump and system, and i could then have rather chosen a smaller pump.
27-03-2008, 02:24 PM #2
Re: Some unscientific considerations of the utilization of vacuum pumps
This is why hose diameter and the removal of schrader cores are important. I have been working on how to connect a 3/8 copper directly to the system.
27-03-2008, 06:21 PM #3
MG,
Back when I worked on "proper" fridge systems, we always brazed in a 3/8" ball valve for just this reason.
Another option is to use a core removal tool and a 1/4"-3/8" F-M flare reducer....
28-03-2008, 03:16 PM #4
I usually braze on some 3/8 going directly to the vac pump then pinch and braze shut after the holding charge of 2psi is put in. Funny seeing the faces of techs trying to figure out what the lone 3/8 process tube is there for!
28-03-2008, 04:03 PM #5
I usually braze in a 1/4" shrader in the suction line if it is only one connection at the suction valve of the compressor. I then have four 1/4" connection, one compressor HP, one receiver and two compressor suction. When I make systems with heat reclaim with 3-way valve and back valves, I braze in additional shrader in the HP lines. Four short 1/4" hoses directly between my 5cfm pump and the system gives a very efficient evacuation. It is also important to evacuate from different parts of the system. I've seen techs evacuate from only the receiver on medium sized systems. It's a long way for the air to flow from the evaporator and suction line through the TEV, the smal pilot opening in the solenoid valve and the liqiud line to reach the receiver. As mentioned, removing of valve cores and valve openers int the hoses is also important. I see the benefit of brazing in 3/8" or even 1/2" conections on larger systems.
28-03-2008, 04:11 PM #6
most certainly, I fail to mention I evac from both high and low side, the 3/8 direct line is on the low side and the 1/4 line goes to high side, all so acr soft copper.
Using copper helps as less off gassing from the lines happens unlike with a service hose.
vacuum timeline
By phicks1065 in forum CommercialReplies: 11Last Post: 12-01-2008, 10:10 PM -
Vacuum pumps
By Andy AC in forum Tools and CalculatorsReplies: 9Last Post: 04-03-2007, 10:24 PM -
Vacuum test
By Peter_1 in forum FundamentalsReplies: 15Last Post: 13-10-2006, 09:04 PM -
Vacuum pumps
By mick2me in forum Air ConditioningReplies: 19Last Post: 28-07-2006, 03:56 PM -
All you ever wanted to know about vacuum pumps
By star882 in forum Refrigeration BooksReplies: 0Last Post: 27-12-2005, 01:44 AM