27-03-2008, 10:18 AM #1
Pressure Test Procedure
Hi all, this is as you can see my first post. Im not a fully qualified engineer yet im still an apprentice so please go easy on me .
I have been looking for a correct Pressure Test Procedure and i cannot find one anywhere!
Can anyone help me?
Thanks, Ross.
-
27-03-2008, 10:28 AM #2
Re: Pressure Test Procedure
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
27-03-2008, 12:53 PM #3
Re: Pressure Test Procedure
.
You need to obtain and read the European refrigeration safety standard, EN 378, specifically part 2 that deals with the levels of pressure testing.
If your equipment falls within the Pressure Equipment Directive (PED), this standard is the one that you HAVE to use.
.
-
27-03-2008, 01:53 PM #4
Re: Pressure Test Procedure
Hi Ross and welcome to the best Hvac site around,,..You can learn alot from the boys and girls on here,,.Anyway im sure you college teacher should be going through all that with you.!!
-
27-03-2008, 04:20 PM #5
Re: Pressure Test Procedure
Thanks for the help everyone. I would have tried to get the information from the college lecturer but he likes us to get on with things ourselves instead of asking him all the time!
-
31-03-2008, 05:22 AM #6
Re: Pressure Test Procedure
Last edited by Brian_UK; 31-03-2008 at 11:50 PM. Reason: Corrected 'quoted' part layout
-
01-04-2008, 04:12 PM #7
Re: Pressure Test Procedure
If it ain't broke, it doesn't have enough features yet.
Damo
-
03-04-2008, 04:48 AM #8
Re: Pressure Test Procedure
Ross, In the land of OZ we have a set of standards which set out minimum design temperatures for testing refrigeration/airconditioning equipment. Basically with a design ambient of 32 degrees C , max test pressure for the high side with an air cooled condenser is the equivalent pressure for the refrigerant used at55 degrees C and for the high using a water cooled condenser the equivalent pressure for the refrigerant at 43 degrees C. Low pressure side test pressure equivalent to 32 degrees C of the refrigerant being used. Sawtell
Similar Threads
-
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM