27-03-2008, 05:29 AM #1
simple suction/ head pressure
please help i keep getting told different things by diffrent people, but can some one please explain in degrees celsius and psi, the correct way to measure the head pressure adn suction pressure, of air conditioning, fridges, so 0 degrees to 7 and freezer down to minus 20
i think head pressure is ambient temp plus between 15- 19 degrees but i get told different every time, tahnks for your help.
-
27-03-2008, 11:02 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: simple suction/ head pressure
Here is answer to me from lana
Here are some figures :
Tai ----- air entering temperature
Tao -----air outlet temperature
Te ------Evaporating temperature
Twi ------water entering temperature
Two-------water outlet temperature
Tc---------condensing temperature
Air conditioning (evaporator) :
Tai-Tao = 8 to 10 °C
Tai-Te=16 to 20°C
Tao-Te=8 to 10°C
Refrigeration (evaporator) :
Tai-Tao = 3 to 5 °C
Tai-Te=5 to 10°C (evaporator TD) take low TD for high relative humidity
Tao-Te=3 to 5°C
Water Chiller (evaporator) :
Twi-Two=5°C
Twi-Te=10°C (evaporator TD)
Two-Te=5°C
Air cooled condenser :
Tao-Tai=5 to 10°C
Tc-Tao=5 to 10°C
Tc-Tai=10 to 20°C (condenser TD) take low TD in design for hot climate so the condenser will be bigger.
Water cooled condenser :
Two-Twi=5°C
Tc-Two=10°C
Tc-Twi=15°C (condeser TD)
Evaporation pressure should be as follow: temperature of air entering to evaporator -TD of evaporator converted to pressure of used gas.
Condensation pressure should be as follow: temperature of air entering to condenser + TD of condenser converted to pressure of used gas.
http://www.refrigeration-engineer.co...9063#post99063Last edited by nike123; 27-03-2008 at 11:20 AM.
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM -
Suction pressure problems on TS units at low ambient temps
By nova in forum TransportReplies: 10Last Post: 18-03-2006, 07:35 PM -
MV600 head pressure trip (ghost)
By andre_fridge in forum Technical DiscussionsReplies: 9Last Post: 28-01-2006, 02:16 PM