Results 1 to 24 of 24
    Feb 2008
    Sudan
    89
    DAIKIN Drain Pump
    Greetings all.
    I am carrying out the installation of more than 300 indoor unit and it is very important to know if there is a check valve in the indoor units (with drain pump) or not?
    11,025
    Re: DAIKIN Drain Pump
    They do not normally have a check valve as far as I know.
    The discharge pipe from the unit should ALWAYS fall towards a the drain outlet.
    The pump is not designed to pump against a large head of water.
    Jan 2006
    Adelaide , Australia
    192
    I agree with Brian UK , no check valves even on the cassette model as that has a pump but only to lift 300mm then gravity must be involved from there to the outlet of the drain .
    If I was putting in 300 of something I would be expecting an answer
    from the supplier or Daikin
    60% of the time it works everytime.
    May 2006
    Sussex
    362
    There is some info here that might help, plus your local Daikin contact details etc.
    http://www.daikinme.com/downloads/default.jsp
    Feb 2008
    Sudan
    89
    Is that means it is unnecessary to install a check valve?
    Why I want to install a check valve? To prevent the water back flow in multiple drain pipes case.
    I want to discuss this point, Is it necessary to install a check valve?
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by 2007eng View Post
    No it is not necessary to install check valve.
    You need to lay condensation pipes in order that you ensure proper drain of water from them by gravitation.
    That mean that condenser pump only lift water column to higher point (approximately 0,5 m is max, consult commissioning literature) immediately at location of indoor unit and from that point it should drain itself by gravitation to collection point or collection pipe who must be at lower point.
    Nov 2006
    Guernsey
    65
    237
    When installing multiple drains and they 'tee' into drains from floor levels above, this can lead to a problem of water leaking from the fan coils on a lower level if a drain blocks elsewhere. Rare, but it does happen! I sometimes install a waterless trap HEPvO type into the condense drain if the indoor fan coil is located above sensitive equipment to prevent this from occuring. I always install this type of trap at the end of the condense drain before it enters a soil or rain water pipe.
    Feb 2008
    Sudan
    89
    Quote Originally Posted by Refrigerologist View Post
    This is the reason of my check valve idea.
    Your solution is very nice, but what is the solution if a drain blocks elsewhere in the floor central drain pipe while the situation of working of indoor pumps and one or more of them is off?
    11,025
    Can you run separate drains from each floor to get around that problem?
    Feb 2008
    Sudan
    89
    No I can't. But this is not solution. I am talking about a leaking from any indoor unit to another if a drain blocks elsewhere in the floor central drain pipe before it enters a rain water pipe.
    11,025
    Well then, run separate drains from each unit to a tundish adjacent to the main drain point. That way there will not be any interaction between the units.
    Also, correct maintenance of the drains will/should ensure good performance.
    Feb 2008
    Sudan
    89
    Nice Brian_UK, But I have 16 indoor units on the floor and I have 29 floors. What about cost?
    Split Croatia
    57
    6,151
    36
    What kind of pipes you using for condensate drain?
    I usulay using PP pipes for domestic waiste like this:
    http://tinyurl.com/2xax6t
    I usually starting with 32 mm diameters at Fan-coil and gradually raising diameter as number of connections raising (and for large AHUs) and applying same rules as plumbers for layout practice. No siphons and decline of 1% is mandatory. All branch connections to collector pipe must be from above. leak test at commissioning.
    I don't have single case of pipe obstruction or leakage from day one of that practice (more then 10 years).
    Feb 2008
    Sudan
    89
    I usually using PVC pipes starting with 25 or 32 and raising diameter as number of connections raising like u.
    Our service area here about 50 cm from slap to false ceiling and we have a lot of works in this area I can't run separate drains from each unit.
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Mar 2007
    394
    When I have done office installations etc. I generaly ran a couple of main drains in (depending on void depth v drain length v unit drain height (modified by pump head where fitted).
    The drain preferabley copper would be trapped and air broken before joining main drain or other. Individual air breaks for each unit would be achieved by sizing for 15mm or 22mm (depending on unit requirements) draining into open connections on the main condensate drain. If you size the main drain correctly, keep it rigid enough and ensure a good fall (I would suggest no less than 1:40) then you will have no trouble plus its easy to add rodding points and you can intorduce biocide and stuff at any or all the air breaks.
    Nov 2006
    Guernsey
    65
    237
    Generally all condensates are run in 32mm (11/4") pvc waste as per manufacturer's requirements, fall is minimum 1mm in 900mm.
    The waterless trap solution will not cause you any problems elsewhere. If the main drain blocks then the water will back up in the pipe and find its way out of the lowest point, that is the lowest fan coil. Waterless traps can prevent this except for where a large column of water builds up in the main stack and reverses the bladder in the trap. But if the main stack blocks you would be in deep doodoo anyway!! Tundishes can be useful too, but you need to be careful, if a stack pipes back up. I have seen a couple of building flooded due to rain water pipes blocking and water pouring back out throught the tundish!
    The main reason I use waterless traps is they do not dry out in the heating season, so we don't get foul odours coming out of the fan coils.
    11,025
    Have you considered using a vacuum condensate removal system?
    http://www.jetvac.ca/FAQ.htm
    Feb 2008
    Sudan
    89
    Boget...Boget..!
  19. #19
    11,025
    Boget...Boget..!
  20. #20
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, Brian_UK
    Boget...Boget..!
    maybe this...
    http://www.urbandictionary.com/define.php?term=boget
    Best regards, Josip
  21. #21
    Feb 2008
    Sudan
    89
    Sorry I mean Budget.
  22. #22
    merthyr tydfil
    I do this set up day in day out...run a central pipe 1"1/4 from the highest point gradually falling until you t into a soil stack using a strap on boss...... then come off each unit in 3/4 pipe and drop off into the central pipe....
  23. #23
    11,025
    OK, I wasn't sure whether to be offended or not
  24. #24
    Feb 2008
    Sudan
    89
    Don’t worry this is my mistake.Thanks .
  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Last Post: 20-05-2011, 02:18 AM
  2. Daikin lift pump
    By Slim R410a in forum Air Conditioning
    Last Post: 13-07-2009, 11:12 PM
  3. Help with condensor pump
    By Bakerbj in forum Air Conditioning
    Last Post: 14-06-2009, 12:39 AM
  4. frostles heat pump
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Last Post: 29-01-2008, 09:27 PM