    DAIKIN Drain Pump



    Greetings all.
    I am carrying out the installation of more than 300 indoor unit and it is very important to know if there is a check valve in the indoor units (with drain pump) or not?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: DAIKIN Drain Pump

    They do not normally have a check valve as far as I know.

    The discharge pipe from the unit should ALWAYS fall towards a the drain outlet.

    The pump is not designed to pump against a large head of water.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: DAIKIN Drain Pump

    Quote Originally Posted by Brian_UK View Post
    They do not normally have a check valve as far as I know.

    The discharge pipe from the unit should ALWAYS fall towards a the drain outlet.

    The pump is not designed to pump against a large head of water.
    I agree with Brian UK , no check valves even on the cassette model as that has a pump but only to lift 300mm then gravity must be involved from there to the outlet of the drain .
    If I was putting in 300 of something I would be expecting an answer
    from the supplier or Daikin
    Last edited by Toolman; 24-03-2008 at 12:26 AM.
    60% of the time it works everytime.

  4. #4
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    20

    Re: DAIKIN Drain Pump

    There is some info here that might help, plus your local Daikin contact details etc.
    http://www.daikinme.com/downloads/default.jsp

  5. #5
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    Quote Originally Posted by Brian_UK View Post
    They do not normally have a check valve as far as I know.

    The discharge pipe from the unit should ALWAYS fall towards a the drain outlet.

    The pump is not designed to pump against a large head of water.
    Is that means it is unnecessary to install a check valve?

    Why I want to install a check valve? To prevent the water back flow in multiple drain pipes case.
    I want to discuss this point, Is it necessary to install a check valve?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: DAIKIN Drain Pump

    Quote Originally Posted by 2007eng View Post
    Is that means it is unnecessary to install a check valve?

    Why I want to install a check valve? To prevent the water back flow in multiple drain pipes case.
    I want to discuss this point, Is it necessary to install a check valve?
    No it is not necessary to install check valve.
    You need to lay condensation pipes in order that you ensure proper drain of water from them by gravitation.
    That mean that condenser pump only lift water column to higher point (approximately 0,5 m is max, consult commissioning literature) immediately at location of indoor unit and from that point it should drain itself by gravitation to collection point or collection pipe who must be at lower point.

  7. #7
    Join Date
    Nov 2006
    Location
    Guernsey
    Age
    65
    Posts
    237
    Rep Power
    18

    Re: DAIKIN Drain Pump

    When installing multiple drains and they 'tee' into drains from floor levels above, this can lead to a problem of water leaking from the fan coils on a lower level if a drain blocks elsewhere. Rare, but it does happen! I sometimes install a waterless trap HEPvO type into the condense drain if the indoor fan coil is located above sensitive equipment to prevent this from occuring. I always install this type of trap at the end of the condense drain before it enters a soil or rain water pipe.
    Last edited by Refrigerologist; 24-03-2008 at 02:06 PM.

  8. #8
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    Quote Originally Posted by Refrigerologist View Post
    this can lead to a problem of water leaking from the fan coils on a lower level if a drain blocks elsewhere.
    This is the reason of my check valve idea.

    Your solution is very nice, but what is the solution if a drain blocks elsewhere in the floor central drain pipe while the situation of working of indoor pumps and one or more of them is off?

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: DAIKIN Drain Pump

    Can you run separate drains from each floor to get around that problem?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    Quote Originally Posted by Brian_UK View Post
    Can you run separate drains from each floor to get around that problem?
    No I can't. But this is not solution. I am talking about a leaking from any indoor unit to another if a drain blocks elsewhere in the floor central drain pipe before it enters a rain water pipe.

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: DAIKIN Drain Pump

    Quote Originally Posted by 2007eng View Post
    No I can't. But this is not solution. I am talking about a leaking from any indoor unit to another if a drain blocks elsewhere in the floor central drain pipe before it enters a rain water pipe.
    Well then, run separate drains from each unit to a tundish adjacent to the main drain point. That way there will not be any interaction between the units.

    Also, correct maintenance of the drains will/should ensure good performance.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    Quote Originally Posted by Brian_UK View Post
    Well then, run separate drains from each unit to a tundish adjacent to the main drain point. That way there will not be any interaction between the units.

    Also, correct maintenance of the drains will/should ensure good performance.
    Nice Brian_UK, But I have 16 indoor units on the floor and I have 29 floors. What about cost?

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: DAIKIN Drain Pump

    Quote Originally Posted by 2007eng View Post
    Nice Brian_UK, But I have 16 indoor units on the floor and I have 29 floors. What about cost?
    What kind of pipes you using for condensate drain?
    I usulay using PP pipes for domestic waiste like this:
    http://tinyurl.com/2xax6t

    I usually starting with 32 mm diameters at Fan-coil and gradually raising diameter as number of connections raising (and for large AHUs) and applying same rules as plumbers for layout practice. No siphons and decline of 1% is mandatory. All branch connections to collector pipe must be from above. leak test at commissioning.
    I don't have single case of pipe obstruction or leakage from day one of that practice (more then 10 years).

  14. #14
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    I usually using PVC pipes starting with 25 or 32 and raising diameter as number of connections raising like u.
    Our service area here about 50 cm from slap to false ceiling and we have a lot of works in this area I can't run separate drains from each unit.

  15. #15
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: DAIKIN Drain Pump

    When I have done office installations etc. I generaly ran a couple of main drains in (depending on void depth v drain length v unit drain height (modified by pump head where fitted).
    The drain preferabley copper would be trapped and air broken before joining main drain or other. Individual air breaks for each unit would be achieved by sizing for 15mm or 22mm (depending on unit requirements) draining into open connections on the main condensate drain. If you size the main drain correctly, keep it rigid enough and ensure a good fall (I would suggest no less than 1:40) then you will have no trouble plus its easy to add rodding points and you can intorduce biocide and stuff at any or all the air breaks.

  16. #16
    Join Date
    Nov 2006
    Location
    Guernsey
    Age
    65
    Posts
    237
    Rep Power
    18

    Re: DAIKIN Drain Pump

    Quote Originally Posted by 2007eng View Post
    This is the reason of my check valve idea.

    Your solution is very nice, but what is the solution if a drain blocks elsewhere in the floor central drain pipe while the situation of working of indoor pumps and one or more of them is off?
    Generally all condensates are run in 32mm (11/4") pvc waste as per manufacturer's requirements, fall is minimum 1mm in 900mm.

    The waterless trap solution will not cause you any problems elsewhere. If the main drain blocks then the water will back up in the pipe and find its way out of the lowest point, that is the lowest fan coil. Waterless traps can prevent this except for where a large column of water builds up in the main stack and reverses the bladder in the trap. But if the main stack blocks you would be in deep doodoo anyway!! Tundishes can be useful too, but you need to be careful, if a stack pipes back up. I have seen a couple of building flooded due to rain water pipes blocking and water pouring back out throught the tundish!

    The main reason I use waterless traps is they do not dry out in the heating season, so we don't get foul odours coming out of the fan coils.
    Last edited by Refrigerologist; 26-03-2008 at 08:03 PM.

  17. #17
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: DAIKIN Drain Pump

    Have you considered using a vacuum condensate removal system?

    http://www.jetvac.ca/FAQ.htm
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  18. #18
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    Boget...Boget..!

  19. #19
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: DAIKIN Drain Pump

    Quote Originally Posted by 2007eng View Post
    Boget...Boget..!
    ------
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  20. #20
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: DAIKIN Drain Pump

    Hi, Brian_UK


    Quote Originally Posted by 2007eng
    Boget...Boget..!
    Quote Originally Posted by Brian_UK View Post
    ------
    maybe this...

    http://www.urbandictionary.com/define.php?term=boget

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  21. #21
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    Sorry I mean Budget.

  22. #22
    Join Date
    Dec 2007
    Location
    merthyr tydfil
    Posts
    18
    Rep Power
    0

    Re: DAIKIN Drain Pump

    Quote Originally Posted by 2007eng View Post
    Nice Brian_UK, But I have 16 indoor units on the floor and I have 29 floors. What about cost?
    I do this set up day in day out...run a central pipe 1"1/4 from the highest point gradually falling until you t into a soil stack using a strap on boss...... then come off each unit in 3/4 pipe and drop off into the central pipe....

  23. #23
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: DAIKIN Drain Pump

    Quote Originally Posted by 2007eng View Post
    Sorry I mean Budget.
    OK, I wasn't sure whether to be offended or not
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  24. #24
    Join Date
    Feb 2008
    Location
    Sudan
    Posts
    89
    Rep Power
    17

    Re: DAIKIN Drain Pump

    Quote Originally Posted by Brian_UK View Post
    OK, I wasn't sure whether to be offended or not
    Don’t worry this is my mistake.Thanks .

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Daikin lift pump
    By Slim R410a in forum Air Conditioning
    Replies: 10
    Last Post: 13-07-2009, 11:12 PM
  3. Help with condensor pump
    By Bakerbj in forum Air Conditioning
    Replies: 23
    Last Post: 14-06-2009, 12:39 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •