    Oil Accumulation



    hi everyone!
    i'm very new in refrigeration and sometimes some big problems. this one is one of them well, i hope i could get my solution here.

    during the refrigeration cycle, some oil of the compressor flows with the refrigerant.while it is flowing into evaporator from capillary tube, oil accumulation happens in the entry of the evaporator. i wonder how can i prevent the evaporator from oil accumulation.

    i'm sorry for terminology
    thanks.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Oil Accumulation

    Quote Originally Posted by ozankalkan View Post
    hi everyone!
    i'm very new in refrigeration and sometimes some big problems. this one is one of them well, i hope i could get my solution here.

    during the refrigeration cycle, some oil of the compressor flows with the refrigerant.while it is flowing into evaporator from capillary tube, oil accumulation happens in the entry of the evaporator. i wonder how can i prevent the evaporator from oil accumulation.

    i'm sorry for terminology
    thanks.
    Hi, ozankalkan. Welcome to RE.

    By carefully designing system and maybe using oil separator.

    Describe little more your problem and system layout.
    Last edited by nike123; 20-03-2008 at 01:27 PM.

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Oil Accumulation

    question:
    Is the compressor and evaporator on the same level?
    Problems normally occur on poorly designed systems or if the evap is below the compressor.
    Refrigeration engineers solve this through careful design, the rest of us use oil separators!

  4. #4
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Oil Accumulation

    Quote Originally Posted by ozankalkan View Post
    during the refrigeration cycle, some oil of the compressor flows with the refrigerant.while it is flowing into evaporator from capillary tube, oil accumulation happens in the entry of the evaporator. i wonder how can i prevent the evaporator from oil accumulation.
    Until you give us more information as nike has suggested, Let's assume this is a freezer.

    Take a look at the defrost operation of this unit to verify all is working well. I always like to see a minimum of 4 defrost cycles in a 24 hour period.

    Proper defrost cycles are very important in low temperature applications. Excess frost restricts the airflow and reduces coil loading. This can cause oil to be trapped in the evap possibly causing floodback to the compressor.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Oil Accumulation

    Quote Originally Posted by ozankalkan View Post
    during the refrigeration cycle, some oil of the compressor flows with the refrigerant.while it is flowing into evaporator from capillary tube, oil accumulation happens in the entry of the evaporator. i wonder how can i prevent the evaporator from oil accumulation.
    What type of system are you working on and why do you believe that oil is accumulating in the entry of the evaporator?

  6. #6
    Join Date
    Jan 2008
    Location
    turkey
    Posts
    5
    Rep Power
    0

    Re: Oil Accumulation

    thanks for your replies.
    well this problem occurs in refrigerators. there is a capillary tube with heat exchanger. capillary and evaporator tubes are jointed by welding. since capillary diameter size is too smaller than the evap tube diameter, the oil accumulates while flowing into the evaporator tube.
    by the way compressor is below the evaporator, not on the same level.
    how should i design the system? and what is the oil separator?

    thanks again and again.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Oil Accumulation

    Quote Originally Posted by paul_h View Post
    question:
    Is the compressor and evaporator on the same level?
    Problems normally occur on poorly designed systems or if the evap is below the compressor.
    Refrigeration engineers solve this through careful design, the rest of us use oil separators!
    Even the best separators allow some small amount of oil to pass, so eventually it ends up where it shouldn't be... and this brings us back to careful design.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Oil Accumulation

    Quote Originally Posted by ozankalkan View Post
    well this problem occurs in refrigerators. there is a capillary tube with heat exchanger. capillary and evaporator tubes are jointed by welding. since capillary diameter size is too smaller than the evap tube diameter, the oil accumulates while flowing into the evaporator tube.
    Why do you believe that oil is accumulating? What are the symptoms?

  9. #9
    Join Date
    Jan 2008
    Location
    turkey
    Posts
    5
    Rep Power
    0

    Re: Oil Accumulation

    Quote Originally Posted by Gary View Post
    Why do you believe that oil is accumulating? What are the symptoms?
    This is what have been told to me by some experienced engineers. they also told me that they hear some oilish sound while refrigerant is flowing into evaporator.
    Last edited by ozankalkan; 20-03-2008 at 02:40 PM.

  10. #10
    Join Date
    Jan 2008
    Location
    turkey
    Posts
    5
    Rep Power
    0

    Re: Oil Accumulation

    img91.imageshack.us/my.php?image=oilxd8.jpg
    well this is what i try to tell

  11. #11
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Oil Accumulation

    Quote Originally Posted by Gary View Post
    Even the best separators allow some small amount of oil to pass, so eventually it ends up where it shouldn't be... and this brings us back to careful design.
    Even the best compressor fitted with separators sometime seize up, I seem them and read about them all the time.
    Ohh shi..

    Seriously, it was a light hearted response because not much information was given
    Forgive me, I shouldn't have. This is serious business, but it's 11.45pm here and not much to do
    Sorry ozankalkan, at least I got you to tell us whether the compressor and evap where on the same level or not and find out whether you know what an oil separator is.

    edit: this is his image from the above post. Saves people copy and pasting as I can hot link so I hope it makes it up to you.
    Attached Images Attached Images
    Last edited by paul_h; 20-03-2008 at 03:02 PM.

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Oil Accumulation

    Quote Originally Posted by ozankalkan View Post
    This is what have been told to me by some experienced engineers. they also told me that they hear some oilish sound while refrigerant is flowing into evaporator.
    Those experienced engineers are wrong. Any oil entering the evaporator is swept through the evaporator by the flow of refrigerant. Oil does not accumulate at the evaporator entrance.
    Last edited by Gary; 20-03-2008 at 03:01 PM.

  13. #13
    Join Date
    Jan 2008
    Location
    turkey
    Posts
    5
    Rep Power
    0

    Re: Oil Accumulation

    Quote Originally Posted by Gary View Post
    Those experienced engineers are wrong. Any oil entering the evaporator is swept through the evaporator by the flow of refrigerant. Oil does not accumulate at the evaporator entrance.
    So why is there a patent which is named "oil separator for evaporator"?

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Oil Accumulation

    Quote Originally Posted by ozankalkan View Post
    So why is there a patent which is named "oil separator for evaporator"?
    Because it is possible for oil to accumulate in other parts of the evaporator, not the entrance.

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Oil Accumulation

    Would it be possible for a few drops of oil to accumulate as shown in the drawing? Yes. Would this affect the operation? No. It would not be enough to make any difference at all. It is not important.

  16. #16
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Oil Accumulation

    Quote Originally Posted by Gary View Post
    Would it be possible for a few drops of oil to accumulate as shown in the drawing? Yes. Would this affect the operation? No. It would not be enough to make any difference at all. It is not important.
    I agree with Gary.

    If it's an issue you have trying to have a 100% perfect system then just don't insert the cap tube too far in the evap inlet.

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Oil Accumulation

    Do you maybe know what velocity of refrigerant you have in evaporator and what kind of refrigerant you using? Could you explain evaporator design?
    Where is refrigerant injection, at top of evaporator or at bottom?
    Do you have parallel circuits or serial circuits in evaporator?

  18. #18
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Oil Accumulation

    What problem is the oil accumilation at the entry to the evaporator causing? What are the symptoms?
    Is the capiliary blocking up?

    Cheers Jon