    hunting
    hi to all RE eng
    for a new engineer need to know more about system hunting and how to oner come it without changing machine
    best regard
  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    61
    Posts
    331
    Rep Power
    10
    Re: hunting
    Quote Originally Posted by jumanje13 View Post
    hi to all RE eng
    best regard
    jumanje
    Please define hunting.......Expansion valve?
    Regards..........Powell
  3. #3
    Join Date
    Feb 2008
    Location
    egypt
    Age
    31
    Posts
    24
    Rep Power
    0
    Re: hunting
    yes that is lake on system and on/off alot because flashe in liquid and it appears on txv
    i need alot about it
    thank you
    best regards
  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    69
    Posts
    10,484
    Rep Power
    50
    Re: hunting
    If you have a leak in the system then you must fix that first, then recharge the system fully.
    The flash gas is due to the shortage of refrigerant I expect and will cause hunting.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
    Please support http://the100project.net/Home
  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    35
    Posts
    1,646
    Rep Power
    17
    Re: hunting
    there has to be some irony here some where being where he posted this!
  6. #6
    Brian_UK's Avatar
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    69
    Posts
    10,484
    Rep Power
    50
    Re: hunting
    Quote Originally Posted by The MG Pony View Post
    Perhaps we are the last hope
    Retired March 2015
  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    62
    Posts
    2,121
    Rep Power
    23
    Re: hunting
    Hi, all
    Quote Originally Posted by Brian_UK View Post
    .......as usually
    Best regards, Josip
    It's impossible to make anything foolproof because fools are so ingenious...
    Don't ever underestimate the power of stupid people when they are in large groups.
    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.
  8. #8
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    61
    Posts
    331
    Rep Power
    10
    Re: hunting
    Are you stating here that the system (compressor) cycles on/off on the Low Pressure Control or another control?
    Or maybe the condenser fan(s) cycle on/off?
    I'm just trying to narrow this down a bit.
    powell
  9. #9
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    45
    Posts
    1,093
    Rep Power
    17
    Re: hunting
    Hi Jumanji13
    Hunting should only indicate the TEV as if it were the comp or fan that would be shot cycling. So check your superheat - and probs with the valve could be SOG, Blocked strainer at inlet, Lost charge of bulb or poor contact to pipe of sensing element, or stuffed TEV. Check for basics first like touch feel for blockages on LL etc.
    Ps in your next post pls give us a bit more data to go on like system parameters - press/temp/maxmin and some history if you can find and we will help as we can. BTW I will be in Cairo on Saturday, cool.
  10. #10
    Join Date
    Feb 2008
    Location
    egypt
    Age
    31
    Posts
    24
    Rep Power
    0
    Re: hunting
    tnx alot
    strainess is the proplem at all
    the circuit is now clean
  11. #11
    Join Date
    Feb 2008
    Location
    egypt
    Age
    31
    Posts
    24
    Rep Power
    0
    Re: hunting
    we will help as we can. BTW I will be in Cairo on Saturday, cool.[/quote]
    thnx
    nice to see you in egypt
Similar Threads
  1. Hunting Etc.
    By subzero*psia in forum Hobbies
    Last Post: 19-09-2010, 01:40 PM
  2. TXV hunting in a walkin cooler
    By dkemper in forum Trouble Shooting
    Last Post: 15-11-2007, 04:14 PM
  3. Hunting
    By philjd26 in forum Trouble Shooting
    Last Post: 26-09-2007, 06:12 AM
  4. Low System Performance (Hunting ?)
    By rhlg in forum Technical Discussions
    Last Post: 25-10-2006, 01:05 AM
  5. hunting???
    By Friobernal in forum Fundamentals
    Last Post: 18-05-2004, 02:00 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts