    Thumbs up Frequent compressor burn outs



    Dear guys,
    Best Wishes for all of you.
    For the past 5 years i am facing the frequent compressor failures kindly suggest me to over come this failures.

    Attached Files Attached Files



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Frequent compressor burn outs

    What are the conditions with power supply. Burn out are in lot of cases connected with bad power supply.

  3. #3
    Join Date
    Dec 2007
    Location
    india
    Age
    47
    Posts
    7
    Rep Power
    0

    Re: Frequent compressor burn outs

    The power supply is stable. ie 400V (+/- 5 v of variation) and the power failures is twice a week only.

  4. #4
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Frequent compressor burn outs

    Quote Originally Posted by askannan View Post
    and the power failures is twice a week only.
    Twice a week is a lot! Do these compressors have any sort of phase line monitors or surge protection devices installed?

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Frequent compressor burn outs

    Are you cleaning the system after the burn out, have you checked for acid in the system?
    If not there is your problem.

    Ian

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Frequent compressor burn outs

    Quote Originally Posted by askannan View Post
    The power supply is stable. ie 400V (+/- 5 v of variation) and the power failures is twice a week only.
    Twice a week! You certainly need good under voltage and phase loss/rotation protection.
    Also, after change of compressor, did you fitted acid filters and controlled oil acidity, and change them in to normal filter after you assured that there is no acid in oil any more?
    Did you checked and changed contactor when you changed compressor?

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Frequent compressor burn outs

    Word .doc from Askanan
    One of my customer having 300TR x 6nos of Screw chiller. The chiller package consists of 2 Nos vertical hermetic screw compressor. It has to maintain the chilled water temperature of 44 deg. F at ambient temperature of 105deg.F (max). One chiller package having two independent refrigerant circuit (case cade system). This is a flooded type chiller with air-cooled condenser (with fan staging control).

    I am maintaining the discharge super heat below 50deg.F by using the liquid injection. The compressor dose not reach it’s RLA at any circumstances even though these compressors are failing frequently.

    If any one came across this kind of problem kindly tell me what could be the problem. Kindly suggest me what kind of precaution to be taken to avoid this kind of problems.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Frequent compressor burn outs

    Repeated burnouts on the same system is either due to one or two things.

    Either system is not being cleaned out good or the electrical power is terrible. This sounds like a Dunham-Bush screw chiller and it should have phase loss/reversal protection already.

    As nike123 pointed out you should also check the contactor. I have seen some where the power supply was OK on the line side of the contactor, but when energized the load side voltage variation was not good (contacts were burnt from arcing).

    Quote Originally Posted by askannan
    The power supply is stable. ie 400V (+/- 5 v of variation) and the power failures is twice a week only.
    Is this the total variation or only between two phases?
    If all else fails, ask for help.


  9. #9
    Join Date
    Dec 2007
    Location
    india
    Age
    47
    Posts
    7
    Rep Power
    0

    Re: Frequent compressor burn outs

    Quote Originally Posted by powell View Post
    Twice a week is a lot! Do these compressors have any sort of phase line monitors or surge protection devices installed?

    There is Power Control Relay in the circuit which is taking care of phase reversal/ unbalance, phase failures and over /under voltage. Ther is no surge protection device in the system.

  10. #10
    Join Date
    Dec 2007
    Location
    india
    Age
    47
    Posts
    7
    Rep Power
    0

    Re: Frequent compressor burn outs

    Quote Originally Posted by powell View Post
    Twice a week is a lot! Do these compressors have any sort of phase line monitors or surge protection devices installed?

    There is Power Control Relay in the circuit which is taking care of phase reversal/ unbalance, phase failures and over /under voltage.

  11. #11
    Join Date
    Dec 2007
    Location
    india
    Age
    47
    Posts
    7
    Rep Power
    0

    Re: Frequent compressor burn outs

    Quote Originally Posted by US Iceman View Post
    Repeated burnouts on the same system is either due to one or two things.

    Either system is not being cleaned out good or the electrical power is terrible. This sounds like a Dunham-Bush screw chiller and it should have phase loss/reversal protection already.

    As nike123 pointed out you should also check the contactor. I have seen some where the power supply was OK on the line side of the contactor, but when energized the load side voltage variation was not good (contacts were burnt from arcing).



    Is this the total variation or only between two phases?
    It is the total variation

  12. #12
    Join Date
    Dec 2007
    Location
    india
    Age
    47
    Posts
    7
    Rep Power
    0

    Re: Frequent compressor burn outs

    Quote Originally Posted by nike123 View Post
    Twice a week! You certainly need good under voltage and phase loss/rotation protection.
    Also, after change of compressor, did you fitted acid filters and controlled oil acidity, and change them in to normal filter after you assured that there is no acid in oil any more?
    Did you checked and changed contactor when you changed compressor?
    Before fix the new compressor into the burnout system we do throuh clean of the system by usig Trichloro ethylene. after that flush out the system with dry nitrogen. De-hydrate the system during vaccumizing by using strip heaters on the condenser coils. We replace the catch all drier in the oil return line with high acid / burnout core. After re commissioning the compressor we run the compressore for 12 hours and we do replace the compressor oil and catch all drier core. we use fresh refrigerant for this system

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Frequent compressor burn outs

    Did you checked first oil for acidity after replacing it with new one.
    Did you checked new oil after some time for acidity?
    Did you changed/checked contactor?

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Frequent compressor burn outs

    Quote Originally Posted by askannan View Post
    There is Power Control Relay in the circuit which is taking care of phase reversal/ unbalance, phase failures and over /under voltage.
    What make and model is that power control relay?

  15. #15
    Join Date
    Apr 2008
    Location
    Harrisonburg, Va.
    Posts
    16
    Rep Power
    0

    Re: Frequent compressor burn outs

    Don't rule out intermittant flood-back with resulting spikes in amp draw. Those packages had literally no provisions for suction superheat and it was VERY common to experience slugging. Hard to beliveve, but early versions (without automated liquid metering valving) were critically charged and if you over-charged them just a bit, slug they would.

  16. #16
    Join Date
    Apr 2006
    Location
    India
    Posts
    6
    Rep Power
    0

    Re: Frequent compressor burn outs

    I have gone thru your problem statement.
    In the same you have mentioned that you are maintaining superheat less than 50 Deg F which is quite higher.
    Standard superheat setting will be from 15 to 20 Deg F.
    For getting 44degF water temp what is your evap temp or suction pressure? And your discharge pressure?.
    Have you checked the location and operation of TXV bulb for proper superheat?

    Just let me know what are the operating parameters?

  17. #17
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Frequent compressor burn outs

    Quote Originally Posted by kbrohit View Post
    In the same you have mentioned that you are maintaining superheat less than 50 Deg F which is quite higher.
    Standard superheat setting will be from 15 to 20 Deg F.

    He means 50k DISCHARGE superheat - that is the discharge temps are maximum 50K above the saturated condensing temp and he is controlling them with liquid injection.

    Like previously mentioned - have you changed the contactors on any of the comp changes?
    ...and she said "give it to me you big fridgie"

  18. #18
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Frequent compressor burn outs

    Are you sure you are putting compressors for the correct voltage rating back in , or are they wired for the correct voltage , some are star for high voltage and delta for low voltage , I worked on a york chiller a few years ago with dual voltage compressors it had 9 terminals on the compressor and some one got it very wrong .
    also if its part winding start are you getting the sequence right and are both contactors staying in and drawing even amps?

Similar Threads

  1. Looking for thermoking genset take outs.
    By RaFelix in forum Commercial
    Replies: 7
    Last Post: 22-07-2008, 02:04 AM
  2. Reasons for High Pressure / Low Pressure Trip outs
    By majikman in forum Air Conditioning
    Replies: 19
    Last Post: 02-02-2007, 08:47 PM
  3. Frequent Failures
    By abdulazman in forum Trouble Shooting
    Replies: 21
    Last Post: 08-01-2006, 07:40 PM
  4. Motor burn outs
    By bernard in forum Industrial Compressors
    Replies: 8
    Last Post: 25-06-2005, 11:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •