    reciprocating compressor taking heavy jerks on starting



    Hi All,

    M working in data center cooling.
    whenever i start the system compressor take heavy jerks & it is not taking start.If i try 6-7 times it start & cooling is good but after working 1 hour it again trips going low suction pressure.
    I believe liquid is entering inside the compressor.

    Kindly suggest the possible other reasons.

    thank You
    Praveen



  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: reciprocating compressor taking heavy jerks on starting

    praveen,

    More information is required to help you out. Compressor model number would be nice, actual voltage at the job, refrigerant, application and the compressors pressures, temperatures and amperage.

    My SWAG theory would be that it's possibly related to pressure equalization and/or starting components/voltage if it's single phase.

    Regards...............Powell
    Last edited by powell; 16-03-2008 at 04:37 PM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: reciprocating compressor taking heavy jerks on starting

    Does it have a crankcase heater to keep the oil refrigerant free?

    What type of compressor is it ?

    Is it single phase DOL starting or three phase DOL/star delta/part winding start?

    Are the contactors in good shape, no damaged contact surfaces?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2008
    Location
    Saudi Arabia
    Age
    52
    Posts
    69
    Rep Power
    17

    Re: reciprocating compressor taking heavy jerks on starting

    Hi,

    Please check the power supply since we have this probelm lot here , one phase out

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: reciprocating compressor taking heavy jerks on starting

    Quote Originally Posted by powell View Post
    praveen,

    More information is required to help you out. Compressor model number would be nice, actual voltage at the job, refrigerant, application and the compressors pressures, temperatures and amperage.

    My SWAG theory would be that it's possibly related to a pressure equalization and/or starting components/voltage if it's single phase.

    Regards...............Powell
    Add to that the relative location of the components. Is the evaporator higher than the condensing unit?