    Smile Unit coolers using glycol



    Dear All,

    I need some details to my design.

    Plant : Vegetables.
    Refrigerant Ammonia
    Secondary Coolant:38% Prop. Glycol.

    The temp.for the rooms are as follows.

    Raw Goods Vegtables Mixed: 4ºC

    Cleaning & Sorting 4ºC

    Processing 15ºC

    Cleaning of dirty crates 22ºC

    Finished Goods 0ºC

    The above said are customer requirements. We cannot change.

    Basically I consider the Room temp 0ºC and take the glycol temp. as follows

    Temp in to the unit coolers: -14ºC
    Temp Out from the unit coolers:-7ºC

    My Question is
    • Is it possible to attain the room temp 22ºC in the same temperature program.
    • If not what is the solution for that.

    Hope I will get some details.



    Regards,



    TJK



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Unit coolers using glycol

    My Question is
    • Is it possible to attain the room temp 22ºC in the same temperature program.
    • If not what is the solution for that.
    Can you include a condenser coil in the 22°C room to provide heating?

    What is the ambient air temperature in your region? Can ambient air be used for heating?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Unit coolers using glycol

    Remember Relative Humidity is important. The same should be 80 to 85%.

  4. #4
    Join Date
    Mar 2007
    Location
    UAE
    Age
    43
    Posts
    78
    Rep Power
    18

    Re: Unit coolers using glycol

    Quote Originally Posted by Brian_UK View Post
    [/font][/list]Can you include a condenser coil in the 22°C room to provide heating?

    What is the ambient air temperature in your region? Can ambient air be used for heating?


    Ambient Temp:53 C

    The Condenser Coil is placed outside of the cold room only.ambient air be cannot be used for heating.Because The ambieent temp & RH are varying suddenly

    Our Area Is UAE

    Rgds,

    TJK

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Brands unit coolers USA?
    By Friobernal in forum Technical Discussions
    Replies: 6
    Last Post: 06-08-2003, 08:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •