24-06-2003, 10:12 PM #1
Liquid CO2
Okay, I went to the gas distibutor and refilled my CO2 bottle. Now I'm going to build a block to run CO2 through, and see if I can get the -78F.
-
25-06-2003, 01:12 AM #2
First it went great.. I had a minus78F to a minus 80F block (evaporator)... but then the ice (dry ice) started to build up in the evaporator, and as the evap pressure rose, so did the temp
I tried restricting the outlet to reduce the formation of the ice (increase evap press.), but as I did so, the realized temperature increased also... at least I tried it
Maybe I need a CO2 TEV
Nice idea.... poor results.... I'll get some nitrogen, next.
PS: Now I'm driving the overclockers crazy.Last edited by herefishy; 25-06-2003 at 01:16 AM.
-
25-06-2003, 03:27 AM #3Maybe I need a CO2 TEVProf Sporlan
-
25-06-2003, 03:36 AM #4
BTW, triple point for CO2, according to the ASHRAE Fundamentals Handbook, is -69.8°F (60.4 psig). You'll have to keep your evap pressure/temperature above this point to prevent dry ice formation...
Prof Sporlan
-
25-06-2003, 03:45 AM #5
Liquid nitrogen would really open up things up to low temp refrigeration... Its triple point is -346°F (1.82 psia) according to the ASHRAE Fundamentals Handbook.
If you're really going to get serious, try liquid helium. -455.75°F (0.704 psia) triple point. This ought to turn an Intel 8088 into a Cray computer...Last edited by Prof Sporlan; 25-06-2003 at 03:50 AM.
Prof Sporlan
-
25-06-2003, 07:34 AM #6
Cray computer LOL
-
25-06-2003, 03:53 PM #7Originally posted by Prof Sporlan
BTW, triple point for CO2, according to the ASHRAE Fundamentals Handbook, is -69.8°F (60.4 psig). You'll have to keep your evap pressure/temperature above this point to prevent dry ice formation...
Hmmmmm, perhaps an EPR?
-
25-06-2003, 04:48 PM #8
Simple CO2 phase diagram
I am also tinkering with the idea of using CO2 in a cascade. The main problem is it's triple point of -56C/-78F. Staying above this point doesn't make sense; a cascade using R134a in the high stage and R507 (or maybe R410A) in the low stage should be able to reach those temperatures also.
Thus, the question is: how to expand CO2 into an evaporator at 1-2 bara (15-30psia), without the dry ice blocking the expansion device? And then the second big problem: how to efficiently transfer the heat to the metal walls of the evaporator?
-
25-06-2003, 10:43 PM #9Hmmmmm, perhaps an EPR?Prof Sporlan
-
25-06-2003, 10:55 PM #10Thus, the question is: how to expand CO2 into an evaporator at 1-2 bara (15-30psia), without the dry ice blocking the expansion device?
And then the second big problem: how to efficiently transfer the heat to the metal walls of the evaporator?Prof Sporlan
-
26-06-2003, 01:55 AM #11Originally posted by Prof Sporlan
Not sure you will find many epr manufacturers who will readily warrant their products on such a system, though...
Mind you, that I am merely expelling the CO2 to atmosphere. "Triple Point" is an interesting term, which I have never encountered before, though I believe the diagram submitted by DaBit explains it!
Thanks, gentlemen.... I learned something (and I don't say that like I know anything)
I'm considering the capability of the R-404a to reach near -60F, and the potential for the -67F of the CO2, in consideration of, I guess the enthalpy, and the amount of CO2 expended to handle the 120W +/- load. I will reference the appropriate information to to determine the difference in btu/lb of the CO2 vs. R-404A. I may actually be in the process of demonstrating the efficiency of mechanical compression cycle refrigeration?
-
26-06-2003, 04:29 AM #12
There are two saturated states that are noteworthy. One is the critical point. Here, the liquid and vapor phases become indistiguishable. This is the point on top of the P-H dome.
The triple point is the saturated state where the solid, liquid and vapor phases are in equilibrium. This is the "bottom" of the P-H dome.
The bottom of the P-H dome for most substances used as refrigerants is at a very low pressure, and not even a concern for those designing vapor compression refrigeration units. CO2 is an exception.Prof Sporlan
-
26-06-2003, 08:55 AM #13Originally posted by Prof Sporlan
[B]Unfortunately, when you expand liquid CO2 below triple point pressure (60.4 psig), you will make dry ice.
I already was afraid of that. Physical laws cannot be broken.
The Prof isn't an expert on CO2 refrigeration, but he sees significant problems attempting to evaporate CO2 in a refrigeration system below -70°F. In his humble opinion, there are easier ways to design low temp cascade systems.
My preferred low-temp refrigerant for overclocking purposes is ethane. But I had a price quote of $185 excluding VAT, safety fees and transport fees for only 50g (~ 2oz) in a lecture bottle. But still, ethane has some nice properties.
-
19-07-2007, 07:30 AM #14
Re: Liquid CO2
Sorr I'm new.
i need information on how to calculate a evaporator coil for a block ice machine
Regards
Jose
-
19-07-2007, 01:19 PM #15
Similar Threads
-
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Liquid line for multi evaporators
By Kevin Yeo in forum Supermarket RefrigerationReplies: 1Last Post: 29-12-2005, 02:29 PM -
Parker levels in ammonia systems
By Friobernal in forum IndustrialReplies: 3Last Post: 04-08-2005, 03:46 PM -
Liquid Refrigerant Pumping
By bersaga in forum Technical DiscussionsReplies: 34Last Post: 09-08-2003, 08:07 PM