06-03-2008, 07:49 PM #1
Packaged unit
I used my digital gauge's today for the first time since buying them last friday on a packaged AC unit that hadn't run for a while.
Firstly i turned the controller on to cooling and checked the supply grills to see what temperature i was getting off, which i found to be 15C with a room temp of 22C.
I checked the coil was clear and the fan was rotating and also that the compressor was running- which they all were.
Next i connected the gauges and found the Suction pressure at 3.2 bar -7C and the discharge at 9 bar or 38C, it was on R22 by the way, i though this was pretty low and normally i would add some refrigerant but i thought i would check the subcooling first which turned out to be 7K. then i checked the superheat and found it to be 48K.
The evaporator was obviously being starved so i looked for anything that could indicate a blockage i.e a filter drier or expansion device.
I noticed that the sensing phial wasnt strapped properly to the suction pipe and that there was no insulation around the phial.
I strapped the phial back to the pipe and insulated it then ran the unit back up and checked the superheat... this was now 3K. I know this isn't really enough but i thought i would then check the supply air off in the room which was 9C.
Although the pressures are still low and the SC and SH are a little bit low i did'nt add any additional refrigerant as the supply air was as per spec, what do you guys think?
It just goes to show that by using superheat and subcooling you can find the cause of the problem a lot easier in my opinion, instead of just guessing.
The difference between genius and stupidity is that genius has its limits.
Marc
-
06-03-2008, 08:30 PM #2
Re: Packaged unit
Well done Marc, yes you've proved that taking the right set of readings helps no end with analysis of a system. Also a good visual inspection always pays off.
A lesser man would have bumped in some more gas hoping to get both the pressure and the superheat that he wanted.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
06-03-2008, 08:39 PM #3
Re: Packaged unit
With a unit running in cooling at these ambient temperatures, you can't expect it to be performing anywhere near it's design, and pressures will seem low compared to peak design performance.
What you really should do is ignore 'what pressure you think it should be' and stick to temperature measurements.
Well done Marc
-
06-03-2008, 09:13 PM #4
Re: Packaged unit
Thanks guys, i think i'm getting the hang of this A/C melarchy
The difference between genius and stupidity is that genius has its limits.
Marc
-
06-03-2008, 09:54 PM #5
Re: Packaged unit
Ahhh... I see you've been doing your homework.
Good job.
-
06-03-2008, 10:10 PM #6
-
07-03-2008, 12:05 PM #7
Re: Packaged unit
Hey Marc5180.You would be even more impressed with yourself that not just doing the essentials and proper checks and locating the problem...your new digital gauges actually delivered!! Good money well spent...
-
07-03-2008, 04:46 PM #8
Re: Packaged unit
Under low load and low ambient conditions, we might expect the superheat to be on the low side. The low superheat means the coil is fully flooded, thus working efficiently and effectively. The only drawback is possible flooding of the compressor, and low load/low ambient conditions is where floodback is most likely.
Liquid droplets disappear at about 10F/5.5K SH. Most compressor manufacturers recommend a minimum of 15-20F/7.5-11K SH at the compressor inlet.
If the compressor inlet SH is less than 15F/7.5K, then you may want to tweak the TXV in just a little in order to safeguard the compressor.Last edited by Gary; 07-03-2008 at 05:00 PM.
-
07-03-2008, 06:19 PM #9
Re: Packaged unit
The difference between genius and stupidity is that genius has its limits.
Marc
-
07-03-2008, 07:13 PM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
07-03-2008, 07:57 PM #11
Re: Packaged unit
: Originally Posted by: marc5180
So you don't think it low superheat due to a lack of refrigerant?.
It is when a system has low to no subcooling (no reserve) and high superheat (not enough to flood the coil) that we know it needs refrigerant.
: Originally Posted by: marc5180
I didn't want to touch the TXV because i always thought it should never need adjusting unless you are first commissioning the system.Last edited by frank; 08-03-2008 at 01:48 PM.
-
08-03-2008, 01:52 PM #12
-
16-03-2008, 05:37 PM #13
Re: Packaged unit
Sorry about the late reply, i've been on holiday and just arrived back.
Thanks for all the repliesThe difference between genius and stupidity is that genius has its limits.
Marc
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
SL/SB-400 Pump Down Procedures
By absolute-zero in forum TransportReplies: 1Last Post: 29-01-2008, 09:27 PM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM