    Fcu Inside Electrical/ups Rooms



    HI there...

    Can anybody tell me if its permitted to place a FCU inside electrical room and UPS room?? As far as I know only split unit is allowed inside electrical rooms... What about UPS rooms? Can you please inform me?? Is any NFPA rule that gives this information??

    Thanks!!!!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fcu Inside Electrical/ups Rooms

    What difference is there between an FCU and a split that makes you query this?

    As far as I know they both contain the same items, or is your FCU a water cooled one perhaps?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    popi's Avatar
    popi Guest

    Re: Fcu Inside Electrical/ups Rooms

    Thank you for your answer...

    The FCU is connecting to a air-cooled chiller...does this makes difference??the type of the FCU depends on the type of the chiller that will be used?? Can you please tell me the chilled water pipes on the fcu are not dangerous to run inside the lectrical room??what about drainage??

    thnaks

  4. #4
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Fcu Inside Electrical/ups Rooms

    Just a couple of thoughts,

    Are there batteries in the UPS room or are they located separately?
    If lead acid, then atmosphere could be corrosive and explosive, which would necessitate special equipment.

  5. #5
    popi's Avatar
    popi Guest

    Re: Fcu Inside Electrical/ups Rooms

    Thank you for your answer... i want to ask in the electrical room with 7 distribution boards and cable trays uncovered is permitted???

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fcu Inside Electrical/ups Rooms

    All chilled water pipework and refrigerant pipework should be insulated and vapour sealed.

    There should not be any condensation problems if it is done properly.

    Condensate drainage from the FCU or Split should also be installed correctly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: Fcu Inside Electrical/ups Rooms

    If your customer is worried about potential water leaks, mount the (water)FCU outside the room and run supply & extract ductwork into the room.

Similar Threads

  1. Frost elimination inside a cold storage room
    By Frio1 in forum Fundamentals
    Replies: 33
    Last Post: 16-04-2009, 04:51 PM
  2. Replies: 0
    Last Post: 26-10-2007, 11:10 AM
  3. Porkka cold rooms
    By Andy AC in forum Commercial
    Replies: 6
    Last Post: 29-08-2007, 08:14 AM
  4. inside split a/c systems
    By slothslag in forum Air Conditioning
    Replies: 20
    Last Post: 31-10-2004, 12:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •