13-03-2008, 05:32 PM #1
Fcu Inside Electrical/ups Rooms
HI there...
Can anybody tell me if its permitted to place a FCU inside electrical room and UPS room?? As far as I know only split unit is allowed inside electrical rooms... What about UPS rooms? Can you please inform me?? Is any NFPA rule that gives this information??
Thanks!!!!
-
13-03-2008, 07:57 PM #2
Re: Fcu Inside Electrical/ups Rooms
What difference is there between an FCU and a split that makes you query this?
As far as I know they both contain the same items, or is your FCU a water cooled one perhaps?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
14-03-2008, 07:59 AM #3
Re: Fcu Inside Electrical/ups Rooms
Thank you for your answer...
The FCU is connecting to a air-cooled chiller...does this makes difference??the type of the FCU depends on the type of the chiller that will be used?? Can you please tell me the chilled water pipes on the fcu are not dangerous to run inside the lectrical room??what about drainage??
thnaks
-
14-03-2008, 07:21 PM #4
Re: Fcu Inside Electrical/ups Rooms
Just a couple of thoughts,
Are there batteries in the UPS room or are they located separately?
If lead acid, then atmosphere could be corrosive and explosive, which would necessitate special equipment.
-
14-03-2008, 08:41 PM #5
Re: Fcu Inside Electrical/ups Rooms
Thank you for your answer... i want to ask in the electrical room with 7 distribution boards and cable trays uncovered is permitted???
-
15-03-2008, 12:17 AM #6
Re: Fcu Inside Electrical/ups Rooms
All chilled water pipework and refrigerant pipework should be insulated and vapour sealed.
There should not be any condensation problems if it is done properly.
Condensate drainage from the FCU or Split should also be installed correctly.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
19-03-2008, 01:54 PM #7
Re: Fcu Inside Electrical/ups Rooms
If your customer is worried about potential water leaks, mount the (water)FCU outside the room and run supply & extract ductwork into the room.
Similar Threads
-
Frost elimination inside a cold storage room
By Frio1 in forum FundamentalsReplies: 33Last Post: 16-04-2009, 04:51 PM -
Precautions in installing the cold store door from inside
By smpsmp45 in forum NH3Replies: 0Last Post: 26-10-2007, 11:10 AM -
Porkka cold rooms
By Andy AC in forum CommercialReplies: 6Last Post: 29-08-2007, 08:14 AM -
inside split a/c systems
By slothslag in forum Air ConditioningReplies: 20Last Post: 31-10-2004, 12:24 PM