Thread: chilled water
-
12-03-2008, 11:30 PM #1
chilled water
can water flow be calculated from t/d of flow and return water temp can you recomend book or manual for flow rates
Last edited by martinw58; 12-03-2008 at 11:48 PM. Reason: up date
-
12-03-2008, 11:34 PM #2
Re: chilled water
Yes,
But only if the cooling duty is (accurately) known
-
12-03-2008, 11:36 PM #3
Re: chilled water
Not accurately as other things can effect the readings but some people use this method as a guide, it is better to use an orifice plate and pressure gauges.
Ian
-
13-03-2008, 03:30 AM #4
Re: chilled water
where are you people trained? Water has a specific heat value of 4.192 Kj/kg/s. Go back to basics. Mass x flow x TD. Interpolate with variables and you can extract: for example flow rate
magoo
-
13-03-2008, 05:30 AM #5
Re: chilled water
For chilled and condenser water, the expected temperature drop or rise is normally 8° to 10°. Just like air, water has a temperature drop or rise as it is cooled or heated. As a chiller cools water, the number of gallons per minute (gpm) circulated determines the number of degrees of drop.
The same is true for a water-cooled condenser. An 8° temperature change is proportional to about 3.8 gpm circulated per ton. A 10° change is proportional to about 3 gpm circulated per ton.
For example, if a 25-ton system has a chilled water temperature differential of 8°, then 25 tons times 3.8gpm/ton gives a total estimate of the chilled water flow of 95 gpm.
Normal chilled water supply temperature is in the range of 45° to 55°. This is the correct range of chilled-water supply temperatures for comfort cooling. So if you have the compresor fully loaded and your pressures are within the normal range and you are getting the proper delta T then you are getting the right amount of GPM flowLast edited by wambat; 13-03-2008 at 05:40 AM.
-
13-03-2008, 09:37 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: chilled water
Please put some units here. You are giving temperature degrees without indicating of what scale.
That way, all of us from around the world, will be able to understand you.
You know, we are engineers here and such freedom of interpretation is to much for ours non-poetic brains.
-
13-03-2008, 09:46 AM #7
-
13-03-2008, 10:52 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: chilled water
Last edited by nike123; 13-03-2008 at 10:55 AM.
-
13-03-2008, 11:27 AM #9
Re: chilled water
Water has a specific heat value of 4.192 Kj/kg/s. Go back to basics. Mass x flow x TD. Interpolate with variables and you can extract: for example flow rate
magoo
I would personally go with POOH on this or most chillers I have seen have binder points and a pressure drop versus flow rate for the heat exchanger.
-
13-03-2008, 01:06 PM #10
Re: chilled water
Assuming T1 to be 12C and T2 to be 6C can you give us a flow rate then Magoo?
The original question states that he wants to determine the flow rate (mass flow).
As the Viking said - it is possible to determine mass flow but you would need to know the duty capacity of the chiller first (Q). Without it you only have 2 parts of a 4 part equation - Q = m c dt
Similar Threads
-
Energy saving in Chilled water system
By psrao in forum Tools and CalculatorsReplies: 5Last Post: 15-01-2008, 06:54 PM -
Honeywell chilled water temperature controller
By Cofreth in forum Technical DiscussionsReplies: 4Last Post: 07-09-2007, 06:32 PM -
Chilled water treatment
By benj in forum CommercialReplies: 1Last Post: 04-09-2007, 04:44 AM -
Refrigerant vs Chilled Water
By baker in forum Air ConditioningReplies: 4Last Post: 16-01-2004, 02:17 PM -
chilled water PHE
By priti in forum Trouble ShootingReplies: 1Last Post: 31-07-2002, 08:25 PM